200 amp main panel with 225 amp sub panel

Still learning electrical;

The main panel outside is 200 amp. The sub panel in the garage is 225 amp. Is that an issue?

How did you determine amperage? What size is the main disconnect? does the sub panel have a disconnect? If the feed wires are the correct gauge 25 amps likely does not create a problem.


main panel outside with main disconnect 200 amp
Sub Panel inside has no disconnect. Label on inside of panel says 225

1 Like

No issue if the conductors between the 200 amp circuit breaker and the panel are the correct size.

4 Likes

You can only rely on the wire gauges to determine service capacity. The 225 rating of the sub panel only indicates the maximum capacity that panel is rated for, not what is currently installed (determined by the feeder wire gauge).

5 Likes

Thank you!

You haven’t provided enough information to be able to give you a definitive answer. If the feeders are on a properly sized circuit breaker, the rating of the breaker in the sub-panel is irrelevant.