Yesterday I came across an Electrical Meter, on a 1913 house, with 30 Amp written on it. Previously I had only known of meters going down to 60 amp. Anyone else ever seen this before? Does this in fact mean that the service is 30 amp?
Someone had actually installed a 100 amp service panel in the house. Of course, I’ve recommended further evaluation and upgrade.
OK guys, I think I have posted a question like this on the old board and it got a lot of flack but here it goes again…
As a general rule of thumb (not carved in stone):
Round meter box - Up to 60 amp service rating through meter
Square meter box - Up to 100 amp service rating through meter
Rectangular meter box - greater than 100 amp service rating through meter
This is at a glance, not to forget the rating of the wiring or other limiting factors.
Ex: if all wiring is of adequate size if I saw a round meter box and then went to the main breaker box and saw a 150 amp main breaker with nothing in between. I would suggest that this be reviewed by … for safety concerns due to the fact that the main may not trip before the meter would have problems… (I would use proper wording)
I had a similar situation this morning. Round Meter, Square Box, 100 amp service upgrade. #3 AWG copper service feeders to 100 amp main. Meter had me stumped.