Hello evryone ! I have a quick question regarding an A/C unit at an Inspection today. Sorry I don’t have a pic but I will describe it the best I can.
The A/C unit has no disconnect next to it. There is a breaker for the A/C unit in the Service Panel located approx. 30 feet away on the same wall. The panel itself is a Square D all in one(Meter and panel) and is kind of a b**ch to open if you are not familiar with this type. Anyway, back to my question. Does there need to be a disconnect closer to the A/C unit?
I know the IRC and NEC state that the disconnect needs to be in sight of the condensor. I am recommending having a disconnect installed next to the unit.
Hi Brian. My recommendation is based on the fact that the disconnect isn’t TRUELY in sight of the condenser. Even though I know and the Client knows that there is a breaker in the Service panel (which is located on the same wall and in sight of the condenser) dedicated to the A/C.
Would you have done anything differently? I am always trying to learn something from you guys out there!
A breaker in a service panel 30 feet away would be just fine by me and I would not even remotely think to write that up as deficient in any way. Anything more would really be nit-picking I think. Wouldn’t you say the attached example is OK?
In this application if the outside unit is on the same wall as a exterior panel and " Within Sight" then it should be fine.
Keep in mind that their is a limit to within sight…it is 50’ and no more…check out how the NEC defines " In Sight From" to up to 50’…so keep that in mind…their is STILL a limit to “within sight”
That is a service disconnect is it not? So yes that is ok by me.
What does the IRC say about condensers? I do not think the breaker in the main panel counts for condensers does it? I do not think even a lockable breaker counts. Hey, I have already miss read this post once, so what do I know.
One, I do believe a breaker in a main panel within sight of the condenser is sufficient. I can’t find a reference to that in the IRC right now but I’ll keep looking. Two, I think the original question was asking if it was OK that the breaker that was admittedly within 30 feet of the condenser was behind a panel cover and therefore ‘not within sight’…that’s where I was going with my ‘nit-picking’ remark.
I read it that way too at first Michael. But I think the IRC frowns on a breaker in the main panel being the service disconnect. But, I have been wrong before.
Yep. A disconnect can be a breaker, switch, pull-out, etc., etc., and it doesn’t matter if it’s in a service panel, remote panel, switch or fuse box or whatever. It just needs to be accessible and within sight.