Michael,
I’ve gone Desi, “'splain to me Lucy, how he justifies his interpretation”
I believe a thorough reading of this may change his mind and would be intrigued to see where in Texas this is or would apply in residential construction.
All of the steel framed houses I’ve inspected us NM cable…
2005 NEC—210.12
Arc-Fault Circuit-Interrupter Protection.
(B) Dwelling Unit Bedrooms. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected by a listed arc-fault circuit interrupter, combination type installed to provide protection of the branch circuit.
Branch/feeder AFCIs shall be permitted to be used to meet the requirements of 210.12(B) until January 1, 2008.
FPN: For information on types of arc-fault circuit interrupters, see UL 1699-1999, Standard for Arc-Fault Circuit Interrupters.
Exception: The location of the arc-fault circuit interrupter shall be permitted to be at other than the origination of the branch circuit in compliance with (a) and (b):
(a) The arc-fault circuit interrupter installed within 1.8 m (6 ft) of the branch circuit overcurrent device as measured along the branch circuit conductors.
(b) The circuit conductors between the branch circuit overcurrent device and the arc-fault circuit interrupter shall be installed in a metal raceway or a cable with a metallic sheath.
2008 NEC—210.12
(B) Dwelling Units. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit in family rooms, dining rooms, living rooms, parlors, libraries, dens, sun rooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination type installed to provide protection of the branch circuit.
Exception No. 1: Where RMC. IMC, EMT or steel armored cable, Type AC, meeting the requirements of 250.118 using metal outlet and junction boxes is installed for the portion of the branch circuit between the branch circuit overcurrent device and the first outlet, it shall be permitted to install a combination AFCI at the first outlet to provide protection for the remaining portion of the branch circuit.
The action in these proposals deleted the phrase “supplying outlets” and the word “bedrooms” now requiring AFCI protection for all 120-volt, single-phase, 15- and 20-ampere branch circuits in family rooms, dining rooms, living rooms, parlors, libraries, dens, sun rooms, recreation rooms, closets, hallways, or similar rooms or areas. In addition, the last sentence, permitting branch/feeder AFCI devices until January 1, 2008, has been deleted, and the effect is to now require only listed combination AFCI branch circuit protection.
A new exception has been added permitting RMC, IMC, EMT or steel AC cable to protect the branch circuit to the first outlet with the 6-foot length deleted.
The NEC is an ever-changing, ever-improving document, and these are only some of the most important changes for the 2008 version. For more information, see “Stallcup’s Illustrated Code Changes, 2008 edition”. EC
ODE is a staff engineering associate at Underwriters Laboratories Inc., in Research Triangle Park, N.C. He can be reached at 919.549.1726 or at [email protected]. James G. STALLCUP is the CEO of Grayboy Inc., which develops and authors publications for the electrical industry and specializes in classroom training on the NEC and OSHA, as well as other standards. Contact him at 817.581.2206. James W. STALLCUP is vice president and senior editor at Grayboy.