Originally Posted By: jane molina
This post was automatically imported from our archived forum.



Hi


Sometimes I see a aluminun wire looks like a 10guage with no insulation


around it but can’t seem to follow where it goes when I look at the main panel.


what could this betoo. are aluminum wires used for ground?


Jane


Originally Posted By: tallen
This post was automatically imported from our archived forum.



My Satellite dish has a 10awg alu ground.



I have put the past behind me,


where , however, it now sits, making rude remarks.


www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: pdacey
This post was automatically imported from our archived forum.



If it’s bare aluminum wire lets hope it’s only used for a ground.


I see it used as a ground all the time, usually running between the Service Panel and the Sub panel. Connecting the ground bus from the sub panel to the bus in the Service panel.

Just be patient, Joe, Bob, Mike, Ryan and a few others will eventually come into this thread and we'll all know everything there is to know about un-insulated aluminum wire. ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)


--
Slainte!

Patrick Dacey
swi@satx.rr.com
TREC # 6636
www.southwestinspections.com

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



250.62 Grounding Electrode Conductor Material.


The grounding electrode conductor shall be of copper, aluminum, or copper-clad aluminum. The material selected shall be resistant to any corrosive condition existing at the installation or shall be suitably protected against corrosion. The conductor shall be solid or stranded, insulated, covered, or bare.


250.64 Grounding Electrode Conductor Installation.


Grounding electrode conductors shall be installed as specified in 250.64(A) through (F).

  • (A) Aluminum or Copper-Clad Aluminum Conductors. Bare aluminum or copper-clad aluminum grounding conductors shall not be used where in direct contact with masonry or the earth or where subject to corrosive conditions. Where used outside, aluminum or copper-clad aluminum grounding conductors shall not be terminated within 450 mm (18 in.) of the earth.



    Jerry Peck


    South Florida

Originally Posted By: pdacey
This post was automatically imported from our archived forum.



Oh yeah… and Jerry. nachi_sarcasm.gif



Slainte!


Patrick Dacey
swi@satx.rr.com
TREC # 6636
www.southwestinspections.com

Originally Posted By: dbowers
This post was automatically imported from our archived forum.



Jerry -


Was that a yes or a no.


Originally Posted By: dbozek
This post was automatically imported from our archived forum.



Jane…Jerry about summed it up and thanx for that Jerry. Aluminum can be used as a grounding conductor as long as it is properly sized as well. Copper can handle more than aluminum so one has to be careful here. Also as Jerry’s response mentioned, all aluminum wires have to be protected from corrosion. There are anti-oxidant substances out there specifically designed to do just that. Just a suggestion for HI’s…if there is no visible anti-oxidant on an aluminum connection, it should be noted. The absence of such can cause problems down the road. If anything, please refer that it be checked by a qualified electrician.



You cannot help men permanently by doing for them what they should and could do for themselves. Abraham Lincoln

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



Dan,


That was a "Yes" and a "No", depending on what, where, and how.

I thought that part of the code was pretty much self-explanatory (unlike many sections), so I did not add to it.

However, here it is:

250.64 Grounding Electrode Conductor Installation.
Grounding electrode conductors shall be installed as specified in 250.64(A) through (F).

WHAT - (A) Aluminum or Copper-Clad Aluminum Conductors.

WHERE - Bare aluminum or copper-clad aluminum grounding conductors shall not be used where in direct contact with masonry or the earth or where subject to corrosive conditions.

HOW - Where used outside, aluminum or copper-clad aluminum grounding conductors shall not be terminated within 450 mm (18 in.) of the earth.


--
Jerry Peck
South Florida

Originally Posted By: jane molina
This post was automatically imported from our archived forum.



Thank ya all


Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Todd


"My Satellite dish has a 10awg alu ground."

10AWG copper is the minimum if you are talking about bonding.

Mike P.


Originally Posted By: tallen
This post was automatically imported from our archived forum.



I am talking about what came with the dish. It is conected to a ground rod.



I have put the past behind me,


where , however, it now sits, making rude remarks.


www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Todd


Again it must be a 10 AWG 'copper' minimum.

Lowes sells 4' ground rods for dish(s). It is wrong.

Mike P.


Originally Posted By: tallen
This post was automatically imported from our archived forum.



I guess I will call the dish company then. I don’t remember saying it was right or wrong. Just what the situation was.



I have put the past behind me,


where , however, it now sits, making rude remarks.


www.whiteglovehomeinspections.net