Does anyone know if there is a code requirement for this when an AC unit (coil/fan) is installed in the attic?
–
“I have never met a man so ignorant that I couldn’t learn something from him.”
Galileo Galilei
system
(system)
#2
Originally Posted By: bsumpter
This post was automatically imported from our archived forum.
yep. IRC
#1305.1.3.
1) Max distance from opening = 20'
2) Solid floor from access door is 24" mimimun width
3) A mim 30" x 30" level platform in front of the service side
--
"In the fields of observation, chance favors only the mind that is prepared"