Bath fan/light in shower?

I inspected a 1974 SFR yesterday and there was a bath fan/light inside the shower which did not appear to be wet rated by looking at its design. There was a GFCI switch (no outlets) next to the toilet protecting this circuit.

If this fan is not wet rated, I don’t believe having the GFCI protection would be acceptable for this to be ok. Do any of you recognize this fan as being wet rated and/or do you believe this is acceptable with the GFCI protection if it isn’t wet rated? I do not.

The way I look at it is…I wouldn’t use a GFCI protected outlet in a shower :high_voltage: :high_voltage: :high_voltage:



If the GFCI worked and cut the power to the fan and light, I wouldn’t mention it. However, I would recommend not changing the light bulb while taking a shower. :wink:

10 Likes

The label (with any rating) is probably inside the cover with the bulb you wouldn’t want to change while showering.

2 Likes

Looks like someone got confused about which ceiling was over the minimum height above the shower floor!

2 Likes

(post deleted by author)

2 Likes

Didn’t read the info at my link, did ya?
Also, note the exact position of the fixture in relation to the perimeter of the shower stall.

Above a shower or tub is an exclusionary zone for hanging fixtures and paddle fans. It extends out 3 foot from the edge of the area and to a height of 8 foot above the rim.

Above a shower or tub is not a wet location using the NEC definition.

2 Likes

My understanding, after review, is that the exhaust fan/light in my shower that I posted above IS allowed due to it being rated for “damp” locations, is not located in a “wet” location, and is not one of the excluded luminaires mentioned, correct?

The GFCI circuit is a “bonus” safety feature?

1 Like

It would need to be damp rated. The instructions will call for GFI protection. It is not one of the prohibited fixture types.

4 Likes

Thanks for clarifying Jim, much appreciated! :+1:

1 Like

I agree, it’s a damp location and almost all bathroom exhaust fans are damp location rated. GFCI protection is not required by the NEC for a fan in this location however the manufacturer’s instructions may require GFCI protection when iinstalled above a tub.

3 Likes

I fully concur!!!
It may become a most shocking experience if that circuit or those electrical devices are not protected with ground fault mechanisms, or at least an EMT and an ambulance at the ready!

Check mfg install instructions. Some of those fan/light assemblies are not permitted to be used inside the footprint of a bath or shower. (That all depends upon the manufacturer. Different manufacturers may have different ideas about it.)

3 Likes