Boiler-Natural Vent through Foundation Wall / Propane Regulator Vent
Hi all-
2 things i have not see before…appreciate feedback information
  1. Propane regulator- looks like vent is extended by pvc pipe>>Assume is this due to generator?
    If yes- does anyone have clearance/requirement info?
  2. Boiler- Natural vent connects to B-vent through foundation/not terminated above the roof.
    Have never seen installed through foundation/terminated roughly 48"… I am familiar with through the roof spec. Trying to find anything that states can not be through foundation/terminated so low…etc
    Anyone have any reference info?
    I appreciate it.
    Thank you
    2024-6-14-45.1
The regulator vent is fine IMO.
The B-vent is wrong and I would write it up as improper installation and as a potential burn hazard.
Thank u kevin. Do u happen to have any documentation that confirms what makes it not acceptable?
I like to educate myself…
Appreciate it.
Besides the obvious potential burn hazard, I would recommend checking the MFG installation instructions for the boiler.
Untitled1
The “crime” may be the elbow at the vent cap. The cap should be vertical. I don’t think there is a code against B-vent flue going up the side of the house. The vertical section must be the same length or longer than the “horizontal” run and most flue designs have only two 90-degree elbows.
Would this apply to this installation Lon? @lhenderson2
@kleonard This is the one I keep on my clipboard. Same as yours, but includes the roof pitch table, along with flat roof applications.
Couple update points…
  1. Boiler installed 1993/94 (+/-30yrs old)
  2. Found boiler manual (https://www.weil-mclain.com/sites/default/files/field-file/he-ii-manual_1.pdf)
    Looks like sidewall venting was ok per manual
  3. Nothing shows for exposed flue and termination options shown are elbow or hood
Yeah…I thought about the 2-10 rule, also. The manufacturer’s instructions should describe what’s allowed, but I think you are correct about calling out a 2-10 violation.