That’s correct Jim. As you know there are two basic scenarios with metallic water piping systems.
- If where the metallic water pipe entering the structure is buried 10’ or more and qualifies as a grounding electrode with a full interior metal piping system.
- Is when the water pipe entering the structure is non-metallic but the interior piping system in metallic.
In the first scenario the water pipe is an electrode and a GEC or bonding jumper must connect to it within 5’ of where it enters the structure. If there is a meter present (typically near the entry of the pipe) a bonding jumper must be installed around the meter.
In the second scenario the water pipe entering the structure is non-metallic so it is not an electrode but since the interior piping system is metallic then it must be bonded to the electrical system. The bonding connection can be at any location on the water piping system. It is not required to be bonded within the first 5’ of where the water pipe enters the structure.
Also a system made up of non-metallic and metallic piping is not a metallic piping system so bonding of the sections of metallic piping is not required.