Please explain to me what the green screw does for the main service panel ? Please explain to me what the bonding strap does? When is the bonding screw required and when is the bonding strap required ?
Are both bonding strap and bonding screw required in a GE main service panel ? As you can see the service wiring is two hot, a neutral and ground rod. Just wanted to make sure I understand.
Thank You In Advance
Yes, either a bonding strap or a bonding crew would be required in a service panelboard. The strap or screw, called the main bonding jumper, connects the equipment grounding conductor to the service neutral conductor to provide a low impedance path to open an OCPD during a ground fault.
Ah that strap at the top is nothing more than a connection between the neutral bar on the right to the neutral bar on the left. There is no visible main bonding jumper in the photo’s.
4 Conductors supplying this panel enclosure and panelboard itself
No Main Bonding Jumper
lack of knowledge to mark the grounded conductor (at all)…lol…just had to add that.
I would indeed say this is more than likely a Remote Distribution Panel (RDP), if this is the case they need to remove that bar you are asking about…and then re-configure their grounded and grounding conductors accordingly and connect the grounding bus to the enclosure…or without getting into a list, Defer for a licensed electrical contractors evaluation ( hopefully not the one that originally installed it…lol )
But we all know I hate commenting on images with unknown variables…so that is my assumption at this stage…that their is a service disconnection means upstream somewhere.
lol…well I did not read it quite that well…if that is the GEC in that raceway then he has some other things they need to do as well…
I do not like posting on WHAT IF images…without the facts so I will stop giving my comments on them…lol…I think outside the box too much and based on the question I dont want to assume they actually know what a main panel is.