Can Square D breakers be used in a CHALLENGER service panel? The manufactures spec sheet was missing.
Thanks!!
Can Square D breakers be used in a CHALLENGER service panel? The manufactures spec sheet was missing.
Thanks!!
No, Square D breaker can only be used in Square D panels.
T&B may make a classified breaker for Challenger panels.
That is what I thought. The panel also had Cutler Hammer breakers installed but they are permitted in a Challenger panel.