Originally Posted By: Mike Parks This post was automatically imported from our archived forum.
“No floating neutrals.”
When this was installed they may have been no disconnects outside. And if these conductors are under a slab, they are considered outside and can be a three wire set-up.
Originally Posted By: jpeck This post was automatically imported from our archived forum.
roconnor wrote:
As an experienced inspector and educator ... as well a licensed professional engineer ... I see no issue with using the common trade terms. In fact, I think it's actually preferred, unless the difference between the trade and code names would create confusion.
IMHO, the confusion on where the neutral-ground connection (e.g. grounded conductor to equipment grounding conductor connection) goes has nothing to do with what you call a panel ... and it would actually be a "panelboard" and not a "panel". Even using the term "service panel" is not technically correct. The correct term for where the neutral-ground bond goes is "Service Equipment" ... as the homeowner says "what the heck does that mean" ...
Robert,
If that is not part of the confusion, then why all the questions about 'should the neutral be grounded at this sub panel?' or, 'should the neutral be grounded at this main panel and not the sub panel?'
The confusion comes in because everyone is trying to figure out if this is: a) a main panel, b) a sub panel, c) does the neutral get bonded at the main panel, d) and the neutral does not get bonded at the sub panel, and f) right???
The answer is: think "service equipment", forget "main panel or sub panel" FOR THIS DISCUSSION. Not for everything, but FOR THIS DISCUSSION.
The neutral is, quite plain and simply, bonded to ground AT THE SERVICE EQUIPMENT. Now that is not too difficult to understand, is it?
Yes, the SERVICE EQUIPMENT many also be a "main panel", but being a "main panel" has nothing to do with deciding whether or not the neutral gets bonded to ground there. Think SERVICE EQUIPMENT. That's where the neutral gets bonded to ground, and only there.
As an experienced educator, I would think you would immediately latch onto the least confusing way to remember something. I.e., Q. Where is the neutral bonded to ground? A. At the SERVICE EQUIPMENT. Q. What about at the main panel? A. Only if the main panel is ALSO THE SERVICE EQUIPMENT. Q. What if the main panel is not part of the service equipment? A. No. Only at the SERVICE EQUIPMENT.
Now, wouldn't that be much easier to explain and remember if you were teaching "AT THE SERVICE EQUIPMENT" and leaving the "main panel" out of it?
Jerry, as an educator I actually find it easier to explain that the neutral-ground connection is at the main service disconnect. I agree it has nothing to do with panels.
– Robert O’Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
Originally Posted By: jmyers This post was automatically imported from our archived forum.
Quote:
90.5 Mandatory Rules, Permissive Rules, and Explanatory Material.
C) Explanatory Material. Explanatory material, such as references to other standards, references to related sections of this Code, or information related to a Code rule, is included in this Code in the form of fine print notes (FPN's). Fine print notes are informational only and are not enforceable as requirements of this Code.
I am reading that FPN's are included in the code as references and are for informational purposes. No where does it state they are part of the codes and they even go as far to say they are not enforceable as requirements of the code.
JM … Actually, the last sentence of that section would be what I would quote to support that FPN’s are indeed part of the code, but just not enforceable …
(Duck)
-- Robert O'Connor, PE
Eagle Engineering ?
Originally Posted By: rray This post was automatically imported from our archived forum.
This thread has gotten me totally confused. Do I understand correctly that the disconnect for any subpanel must be the same amps rating as the main disconnect in the main panel? If so, why?
Here is one of the panels I looked at yesterday at a 6800 SF house. This was the main panel, main disconnect (200 amps) at yellow arrow. Two subpanel disconnects (red arrows) were 100 amps.
The blue arrows point to what looked like two screws (perhaps connecting two separate cables) covered by blue tape. Any idea what's going on there? A unique/non-standard system for connecting two cables together?
This was a general contractor who built his own house, which, of course, always raises red flags.
Originally Posted By: Bob Badger This post was automatically imported from our archived forum.
The subpanel that this thread was originally about was tapped from a 200 amp main panel with out a separate breaker for the sub panel.
In that case the 200 amp main breaker in the service panel was also the only protection for the sub panel, set up that way the sub panel will need to be rated 200 amps or have its own main breaker.
Now in your picture the main panel is 200 amp and it has 2 100 amp breakers feeding the subpanels, set up that way the sub panels only need to be rated 100 amps.
Got it.
Yes, underneath the blue tape was the outline as shown in your pictures. Thanks.
As I start doing these high-end properties, I'm finding some interesting stuff that I'm not familiar with. I grew up in a large, poor family in South Texas, so these new-fangled billion amp panels are something else.