Okay, so I’m not an electrician. This looks like a 150 amp main breaker. Why did they need four of them linked together?


http://www.nachi.org/bbsystem/usrimages/4150amp.jpg

http://www.nachi.org/bbsystem/usrimages/ge.jpg

http://www.nachi.org/bbsystem/usrimages/gepanel.jpg

http://www.nachi.org/bbsystem/usrimages/gepanelwsub.jpg


--
Inspection Nirvana!

We're NACHI. Get over it.

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



Cost.


That is cheaper than manufacturing one big main breaker, sells for less too.

Some service equipment is designed to accept these and there is no room for the larger heavy duty ones.

These should, theoretically, provide the same protection (at least until you get in AIC, and other such stuff).


--
Jerry Peck
South Florida

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



What you have there, more or less is 4 single pole 75 amp breakers.


2 on each phase in parallel, set up common trip, I have a 200 amp GE panel for my service just like this one.

As Jerry said cheaper and more compact, breakers come in frame sizes, 100, 200, 400 etc. a "normal" 150 amp breaker is a 200 amp frame size.


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: jonofrey
This post was automatically imported from our archived forum.



Thank you fellers!



Inspection Nirvana!


We're NACHI. Get over it.

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



John


The egc's and the neutrals are not seperated in the "sub" panel.

Can you display a better picture of the other panel?

Mike P.


Originally Posted By: jonofrey
This post was automatically imported from our archived forum.



Mike, not sure what you meant.


http://www.nachi.org/bbsystem/usrimages/DSCsub812.jpg


--
Inspection Nirvana!

We're NACHI. Get over it.

Originally Posted By: Blaine Wiley
This post was automatically imported from our archived forum.



Egc’s and neutrals look separated to me.


Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



Good Catch Mike, I agree.


It looks like a green bonding screw in place near the bottom of the right side bar.

Also the tie bar is still in place at the bottom of the two bus bars.

I see what looks like a grounding conductor on the 5th terminal down on the left hand bus bar (just under the red 12 AWG)

So it looks like the right number of conductors have been run from the main to the sub 2 Hots, Neutral and Equipment Ground but are not isolated in the sub panel.

The green screw and the tie bar have to go away.


Blaine your post was not up when I started, but I saved the picture to my desk top and zoomed in to really check out the panel.


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: Blaine Wiley
This post was automatically imported from our archived forum.



Bob,


Your eyes are much better than mine! ![icon_biggrin.gif](upload://iKNGSw3qcRIEmXySa8gItY6Gczg.gif) I gotta get to that eye doctor.


Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



bwiley wrote:
I gotta get to that eye doctor.



![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif) Me too, I cheated by opening the picture in a separate viewer and zooming in close.

Bob


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: jonofrey
This post was automatically imported from our archived forum.



So the ground and neutral bus’s should be bonded in the main panel but the bond should be removed in the sub panel.


Do I understand that correctly?


--
Inspection Nirvana!

We're NACHI. Get over it.

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



Yes, that is correct, the only place neutrals and grounds can be joined is at the location of the main disconnect. (Service Disconnect in NEC speak)


Any other location they must be separated, the NEC never uses the term sub panel, but we all do and any sub panel must have isolated neutral bars.

FYI A sub panel is considered as load side equipment.

Code types if interested look to 250.142(B) & 250.24(A)(5)


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: jpope
This post was automatically imported from our archived forum.



Correct me if I’m wrong - The tie bar needs to be removed as mentioned, but then the ground bus needs to be bonded to the sub-panel. It looks like it’s isolated currently. Am I wrong? eusa_think.gif



Jeff Pope


JPI Home Inspection Service


“At JPI, we’ll help you look better”


(661) 212-0738

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



jpope wrote:
the ground bus needs to be bonded to the sub-panel


Jeff I assume you mean the grounding bus (I know it is a pain but we want to be clear)

Then yes you are 100% correct and I should have said that, it totally slipped my mind. ![icon_sad.gif](upload://nMBtKsE7kuDHGvTX96IWpBt1rTb.gif)

It looks like the green bonding screw can be removed from the grounded conductor bus and replaced in the grounding conductor bus.

The problem we have with it wired this way is a good deal of the neutral current will flow on the grounding conductor.

If the load is great enough we can have enough voltage drop on the grounding conductor to raise the potential of the metal enclosure above the potential of ground.

With these to panels this close it would be possible to put a hand on both enclosures and get a shock between them.

Your body would be trying to carry the difference in voltage caused by the voltage drop on the grounding conductor.

This is not likely to happen with the small load in the sub panel and the short length of run, but it could, this is one reason for the separation of neutral and grounding conductors.

It shows up much more in a heavily loaded sub panel farther from the bonding point, as I run into in commercial work.

Bob


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: jonofrey
This post was automatically imported from our archived forum.



Awesome Dudes, thanks again.



Inspection Nirvana!


We're NACHI. Get over it.

Originally Posted By: jpope
This post was automatically imported from our archived forum.



. . . grounding bus . . icon_redface.gif



Jeff Pope


JPI Home Inspection Service


“At JPI, we’ll help you look better”


(661) 212-0738

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



"Good Catch Mike, I agree.’


BIG HEAD, BIG HEAD, BIG HEAD. ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)

I have had good teachers.

Remember this is "my" field of expertise.

Mike P.


Originally Posted By: rpalac
This post was automatically imported from our archived forum.



I’m Impressed with both Mike and Bob


Good eye, great capture on the explanation.
(In commercial loads you also can creat a heat situation between panel grounding-grouned loads)

a different Bob


Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



"I’m Impressed with both Mike and Bob "


Who? Bob? 2000 Bob? ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)

Thank you Mike P.


Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



rpalac wrote:
(In commercial loads you also can create a heat situation between panel grounding-grounded loads)


Thanks for the kind words and yes you are correct on the heating.

Going back to the panels pictured in this post if there was not a copper grounding conductor run between the main and the sub, the grounding would be accomplished through the metal pipe nipple connecting the panels.

This would be OK for grounding but as the neutral is bonded to the can a good deal of neutral current would flow through the metal nipple.

This would lead to heating of the pipe nipple and enclosure.


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum