Disconnect

Originally Posted By: jschwartz1
This post was automatically imported from our archived forum.



http://www.nachi.org/bbsystem/usrimages/D/DCP_3442.JPG ]


[ Image: http://www.nachi.org/bbsystem/usrimages/D/DCP_3443.JPG ]


Thanks,


--
Jay Schwartz
Coast To Coast Home Services, Inc
www.Coasttocoasthomeservices.com
Southeast Florida NACHI Chapter - VP www.floridanachi.org
NACHI - Legislative Committee Member
MAB - Member

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Yes a breaker in the panel can serve as the disconnect.


It has to be 'within' sight.

It would have to be a breaker with an ampacity that matches what the label on the unit requires.

If the label specifies only fuses you have a problem.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: jschwartz1
This post was automatically imported from our archived forum.



Bob,


Thansk for the quick response. The unit is a Goodman. Any thoughts on the fuse or breaker. Model #CLJ36-1 Serial #0100451031

Thanks,


--
Jay Schwartz
Coast To Coast Home Services, Inc
www.Coasttocoasthomeservices.com
Southeast Florida NACHI Chapter - VP www.floridanachi.org
NACHI - Legislative Committee Member
MAB - Member

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



jschwartz1 wrote:
Bob,

Thansk for the quick response. The unit is a Goodman. Any thoughts on the fuse or breaker. Model #CLJ36-1 Serial #0100451031

Thanks,


Ah... sure, do you know where I left my keys? ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)

No, I do not have any idea what that means.

When I wire a unit there are three things I look for on the tag.

1) Voltage

2) Minimum circuit ampacity

3) Maximum Overcurrent protection.

I do not look at model or serial numbers.

Maybe someone else has the info or you could try and get the info from the makers web site.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: jschwartz1
This post was automatically imported from our archived forum.



thanks. i will see what i can find out.



Jay Schwartz


Coast To Coast Home Services, Inc


www.Coasttocoasthomeservices.com


Southeast Florida NACHI Chapter - VP www.floridanachi.org


NACHI - Legislative Committee Member


MAB - Member