I am working on my mock inspections, when I came across an interesting situation. A distribution panel, that I inspected had multiple instances of two neutral conductors (both 14 AWG), on one lug. As listed on the distribution panel label, I read it as allowing two (2) 14 AWG conductors, among other options.
A couple of days ago this house was inspected and called out for this. My question isn’t necessarily to say the inspector wrong. If this was an actual inspection did I make a mistake?
Carl, as Robert stated/inferred, the NEC has not allowed doubled Neutrals in many, many decades (contrary to most sparky’s knowledge).
As for the Label… if you look at the bottom of the photo, it states… * = For Equipment Grounding Only