double tap ground wires

Originally Posted By: berby
This post was automatically imported from our archived forum.



http://www.nachi.org/bbsystem/usrimages/f/franflin001_002.jpg ]


Originally Posted By: rmoore
This post was automatically imported from our archived forum.



Most ground/neutral bars are listed for a maximum of two, same size, grounding conductors. Neutrals should be “solo”, and the only occupant of any hole.


Your photo is a little small for these old eyes, but it looks like you have double-tapped neutrals...which would be wrong.


--
Richard Moore
Rest Assured Inspection Services
Seattle, WA
www.rainspect.com

Originally Posted By: berby
This post was automatically imported from our archived forum.



Thanks Moore, I have to make a phone call.