Will do, thanks for the info.

As Jim mentioned you need to look at the tap rules in Article 240. The #6 tap conductors in this case would never see more than the 15 amp load since that’s the size of the CB after the tap. That means that the #6 conductors could only become overloaded for a short duration during a ground fault or short circuit condition. The 400 amp OCPD would still protect the tap conductors in either of those conditions since it would open the circuit very quickly.

The lugs at the bottom are deceiving since each hole is rated for only one conductor but if you look closely you can see that it’s actually two lugs (or a double lug) with two holes.

Here’s a photo of a lug rated for two conductors. You can see the 600MCM-4 and the (2)250MCM-1/0 on the face of the lug:

http://lh5.ggpht.com/_CyClsTSXBMc/SOi6u0cZQ0I/AAAAAAAAAG8/v-hjCp_T48s/Rob's%20Work%20022.JPG

IF all the lugs involved are rated for the condustor sizes used and IF the length of the tap conductors is not more than allowed by the tap rule, and IF the downstream protection for the tap is properly sized, then it could be a compliant installation. The reason that the code specifies maximum lengths for such taps is to guard against overcurrent conditions due to damage, etc. on a longer run. Yes, the breaker at the other end would protect against running overloads, but a problem between the two ends could result in the tap conductors overheating, possible causing major conductor damage and fire. The tap rule is employed extensively in industrial situations, but is often misunderstood by many very experienced electricians.

Frank,
What could happen between the ends that would cause overheating? Wouldn’t the OCPD at the end of the tap eliminate the possibility of the tap conductors overheating?

The 10’ and 25’ NEC tap rules can be applied to any installations, even single family residential dwellings. Although they’re not very common they are permitted. Not sure why you think that they only apply to industrial installations?

 I saw such an installation just this week.

I agree. I’ve seen many an electrician who doesn’t quite understand the nuisances of the various tap rules and installs things that are not code compliant and many times unsafe. One other comment is that in your example of the outside tap conductors, even though they’re permitted to be of unlimited length by the rules of NEC 240.21(B)(5) I still agree with your point. :cool:

I found an illustrated explanation of the various tap rules for any who are interested…
http://www.printthis.clickability.com/pt/cpt?action=cpt&title=Understanding+the+Rules+for+Feeder+Taps&expire=&urlID=416616522&fb=Y&url=http%3A%2F%2Fecmweb.com%2Fnec%2Fcode-basics%2Felectric_understanding_rules_feeder%2Findex.html&partnerID=83297

But dont the wires going into the (AC on this thread) have to facilitate the power they are protected by (100 amps)? Most AC systems have service disconnects and are not protected by a breaker. So it looks as though #10 wire is used on a 100 amp breaker. That is also a defect.

Well the discussion is whether or not a code compliant tap can be made as depicted in the photo in post #5. Since that lug(s) is not rated for more than one conductor the tap cannot be code compliant. There are installations where a #10 conductor can be legally tapped to a 100 amp feeder.

Some of the other stuff in this thread is regarding taps that are code compliant. Sorry if it went off topic a bit.

On a tap the OCP is at the utilization end, not the supply end. Read Article 240.21 to see the rules for taps.

How about this lug double tap feeding meter then a Stab-Lok, aluminum and copper with the sec aluminum strands clipped??

No good. It almost looks like tinned copper (could be wrong) rather than AL, but it’s still no good. . .

Thanks Jeff.

A couple of bushings would be nice too.