jgromkoski
(John Gromkoski, License No. 16000020183)
January 12, 2011, 7:20pm
1
Am I correct in stating that extension cords are not allowed to supply permanently mounted fixtures? Even if they are not buried or penetrating through the wall? I am sure the connection at the ceiling junction box is improper.
Jim_Port
(Jim Port)
January 12, 2011, 7:25pm
3
I don’t think I have ever heard of a fan that is listed for use with a swag kit, nor is the mounting method likely compliant.
The use of the swag kit into the extension cord is improper.
gromicko
(Nick Gromicko, CMI)
January 12, 2011, 7:38pm
4
rmeier2
(Robert Meier)
January 12, 2011, 7:42pm
5
This is what the 2008 NEC has to say. Most improper usage falls under condition (1).
400.8 Uses Not Permitted.
Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
**(1) As a substitute for the fixed wiring of a structure **
(2) Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors
(3) Where run through doorways, windows, or similar openings
(4) Where attached to building surfaces
Exception to (4): Flexible cord and cable shall be permitted to be attached to building surfaces in accordance with the provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
(6) Where installed in raceways, except as otherwise permitted in this Code
(7) Where subject to physical damage
jgromkoski
(John Gromkoski, License No. 16000020183)
January 12, 2011, 7:43pm
6
This was not a commercial property. Would there be a difference though on whether it was allowed or not?
jgromkoski
(John Gromkoski, License No. 16000020183)
January 12, 2011, 7:44pm
7
Thanks all. I’ve got the answer I was looking for.
jhugenroth
(Joe Hugenroth)
January 20, 2011, 9:33pm
8
From yesterday
[ATTACH] [/ATTACH]
I see this all the time. They also ran a cord from this receptacle through the outside wall of the garage to power a fountain
jhugenroth
(Joe Hugenroth)
January 20, 2011, 9:38pm
9
From yesterday. I see this all the time
bkelly2
(Brian Kelly, AZ Cert. # 60234)
January 20, 2011, 9:52pm
10
Jim_Port:
I don’t think I have ever heard of a fan that is listed for use with a swag kit, nor is the mounting method likely compliant.
The use of the swag kit into the extension cord is improper .
I would agree with this.
But I see Ceiling Fans with a Swag Kit here in AZ all the time, often to a Switched Outlet.
(Can’t really use Nicks made up guide as reference for anything either.)
bkelly2
(Brian Kelly, AZ Cert. # 60234)
January 20, 2011, 10:24pm
12
Is it a Permanent Fixture if it is not hard wired?