Federal pacific stab lok breakers

any body have a good write up on stab lok brekards?

Was from the 80s and verbally told the client what can go wrong with them, also told them i’d send them some info on them, and it will be in the report.

but seeing if I could grab a write up. thanks .

If you are following your training, there is this.

https://forum.nachi.org/t/well-it-actually-happened-stablok/233614/96?u=bcawhern1

But the debate is far from settled. My recommendation, read the entire thread prior to making a narrative.

3 Likes

I have a simple narrative that I used with FPE panels.

Federal Pacific Stab Lok electriacl panel observed.

“Federal Pacific Stab Lock electrical panel has a history of issues. Recommend licensed electrician evaluate panel for condition, replacement or ceritification of safe operation of the system.”

I don’t know of any electricians that would sign off on those.

4 Likes

You might also include something to this effect.

“Federal Pacific Stab-Lok breakers may affect the insurability of the property. Check with your intended insurance carrier for more information.”

3 Likes

I refer buyers to this article (that I wrote).

But at this point, it’s no longer if the panel might be dangerous or not, or safe or unsafe, or whatever.

At this point, it’s near impossible to get insurance on a home in California if you have one. Your state may vary.

2 Likes

i sent this to the potential buyer. Federal Pacific Electric Stab-Lok panels are hazardous - Structure Tech Home Inspections

(they plan on walking away from this house, roof is over 20 yrs old, wood foundation is bowing in, area in one room the floor takes a steep drop close to the foundation, they know about the roof, but didnt like the foundation stuff.

wow, those are rare in my neck of the woods. Have any photos?

2 Likes

Evening, Patrick. Hope to find you well.

Which brand please? Federal Pacific or Federal Pioneer?

Mostly related to the breakers.
Panels had issues to.
Consumer Product Safety Commission has shown these breakers to have an unacceptably high rate of failure.
FPE committed fraud by falsifying their UL testing, making their UL listing void.
According to the Inspectapedia Blog and Mike Holt Forum, Challenger bought the rights to Stab-Lok from FPE. When EATON acquired Challenger; they wanted no part of Stab-Lok and required Challenger to liquidate the product line before they took over.
Recommend a licernsed electrical contractor further evaluate and make improvements where required.

Federal Pacific

only photos are the window wells where you could see the green treated wood. it was a finished basement so not much to see. checked all corners with the moisture meter. *(was dry even with no sump pump, and gutters discharged right next to house)

see pics. also 1 wall was bowing in.

1 Like

That’s because there is nothing an electrician can to adequately assess the breakers. The alleged problem is that the breakers sometimes fail to trip. An electrician can put a load on a breaker and it may trip, but that doesn’t that it will trip every time it is supposed to.

Recommending that an electrician evaluate it is a cop out. It causes homebuyers to waste time and money. I tell homebuyers that FPE breakers are a topic of controversy. They can make their own inquiries and draw their own conclusions. As an electrician, there is nothing more that I can assess beyond what I can assess as a home inspector.

Short and sweet…

”Functional. Service panel was a Federal Pacific Electric with “Stab-Lok” circuit breakers. These breakers have been known to fail which is a safety hazard. Consider upgrading the service panel by a licensed electrician”

1 Like