Sorry for my ignorance but can someone define or explain this statement on the panel sticker for me. I’ve searched high and low to no avail except crazy industrial equipment…
It’s on the electrical panel of a modular/manufactured home just under the main breaker. At the exterior there’s another 200AMP panel with a few breakers feeding the interior panel. I do have more pics but just wanted to understand this sticker mainly…
Thanks… and yes they were. I’ve had several modular inspections but hadn’t seen that sticker before. Seems odd that it wouldn’t have to be rated for 200amp minimum since that’s the service main size? It also states “not more than… 100amps”
It is a sub-panel rated for 100 amps max! The sticker is so an idiot does not install overcurrent protection higher than the rated 100 amp panel. Your question illustrates how easy that would be to think that as acceptable.
Well, that’s why I’m here to get some positive feedback :). That sub panel certainly didn’t look to be rated for 200amp but the main breaker looked to be integral to the panel. I’m not the one who wired it, just wanted some clarification for calling it out. Keep in mind that some of us are newer at this than others and I for one really appreciate the positive input we can get from these boards.
To me it just seems like something is wrong. Why have a sticker (a type of which I have never seen before) limiting the panel feeder to 100 amps when the main CB is 200 amps unless someone field installed a 200 CB.
Do you have a photo of the nameplate of the sub panel?
Well, you learn something every day. That’s a new one for me. That certainly didn’t look like a manufacturer’s label and I’ve never seen one, but then I don’t inspect manufactured houses.
I infer it to be that though the panel may be rated for up to 200 amps, the house is only certified for 100. Wny, I don’t know, because I don’t do manufactured housing, but Michael did provide an authoritative source reference.
Thanks for the responses folks! I’m glad a few others were scratching their heads too. I did call it out (of course) and there were a few other electrical issues too. My statement read something like… “blahblahblah inspector was unable to determine if panel was rated for 200AMP feeder and client should consult with and licensed electrician”.
It looked like only a 100 amp panel but the breaker looked built-in though I may be wrong on that one, shhh.
OK…think about this for a second and it will become clear…
The 200A in the remote distribution panel is simply a disconnection means. The feeders OCPD that is supplying this panel is rated for 100A and that is what the sticker is mandating.
You can have a 100A OCPD feeding a panel enclosure with a 200A Main Breaker ( or MLO if you wish) and not be a concern. I will assume it is done in accordance with 550.32(B) and 550.33(B) as stated.