Am I correct in saying that the furnace isnt allowed to have return openings to the garage. Also doesnt the open vents break the fire wall?
The furnace didnt work & it is older. I Recommended a HVAC specialist. Wouldnt it be better if they selaed the outside at the garage and used the returns at the interior rooms? The closet had a opening into the interior but the access was sealed & blocked.
I did note the condensate needing to be discharged properly. Nice trench!!
They are combustable vents, I am not sure about the one at the bottom of the door. The ones in the door are for combustion. Doesnt this violate the fire wall?
I agree with Brian that the door louvers/vents don’t seem to be an issue if the mechanical closet/room has tight drywall for the fire separation (particularly at any pipe or duct penetrations). In fact model codes consider adjacent mechanical rooms with a common door part of the garage (which also kicks in the 18" ignition source elevation requirement). Note that there should be one louver/vent up high in addition to the one shown down low. And if there is an old door to the house sealed and/or blocked, it still needs to be a fire rated solid wood or metal door.
My guess about the grille below the door is that it’s a crawl space vent … that is assuming the house has a crawl space, and not a basement. Although I guess it’s possible it’s a furnace supply register (who knows, maybe the owner works in the garage a lot and figured he would add some heat by pissin in the wind … lol). But you are not suppose to have duct openings in a garage.