Gas B-vent terminates near (bedroom) windows.

Originally Posted By: jgallant
This post was automatically imported from our archived forum.



Is there a standard minimum distance and height combination that a gas appliance “B” vent needs to be from an openable window to prevent exhaust gasses from entering living spaces? A house I inspected today, built in 1993, had a “B” vent terminate level with the bottom edge of upstairs windows, 5 feet from an openable hallway window and 6 feet from an openable bedroom window. Seems like an obvious risk of CO poisoning to me.


![](upload://39I4VPV40KC0qXJ8rPDfv0ICJYj.jpeg)


--
-Jim Gallant
Owner, All Point Home Inspections - Poulsbo, WA www.allpointinspections.com
Co-founder, ReportHost (Web-based report writing service) www.reporthost.com

Originally Posted By: dvalley
This post was automatically imported from our archived forum.



Jim,


This B-vent should be 8 feet away from any vertical wall and two feet above. B-vents should never terminate near window openings.

This vent is in violation of the 3-2-10 rule anyways. ![](upload://dT7PXS8lZhpuVS6c8qAaMebqRVH.gif)It's too short.


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: jgallant
This post was automatically imported from our archived forum.



dvalley wrote:
Jim,

This B-vent should be 8 feet away from any vertical wall and two feet above. B-vents should never terminate near window openings.

This vent is in violation of the 3-2-10 rule anyways. ![](upload://dT7PXS8lZhpuVS6c8qAaMebqRVH.gif)It's too short.



--
-Jim Gallant
Owner, All Point Home Inspections - Poulsbo, WA www.allpointinspections.com
Co-founder, ReportHost (Web-based report writing service) www.reporthost.com

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



David,


The 3-2-10 rule does not apply to B vents with B vent caps. With unapproved caps or vents, yes, 10 feet applies.

8 feet from the wall or 2 feet higher than it for listed B vent sizes 12" and smaller.

Don't know of anything addressing windows, maybe because it is already required to be 8 feet from any wall ...


--
Jerry Peck
South Florida

Originally Posted By: jgallant
This post was automatically imported from our archived forum.



Where does the “8’ away” or “2’ above” rule come from? In case someone calls me on this. NFPA? IRBC?



-Jim Gallant


Owner, All Point Home Inspections - Poulsbo, WA www.allpointinspections.com


Co-founder, ReportHost (Web-based report writing service) www.reporthost.com

Originally Posted By: tallen
This post was automatically imported from our archived forum.



Jim,



It is IRC [2426.6.5] and UMC {806.4}


--
I have put the past behind me,
where , however, it now sits, making rude remarks.

www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



Also comes from the manufacturers installation instructions.



Jerry Peck


South Florida