Do you find anything wrong with the way the TPRV discharge pipe is installed and routed? Do you find anything wrong how the Gas Water Heater is sitting on the garage? Is the distance from the garage floor to the combuation chamber of the gas w/h correct? Or does the w/h requires to be set on a stand higher that 12" from the floor?
I believe it’s 18" off the floor, but check your local rules. That one’s incorrect and considered to be a fire hazard if the garage is used for vehicles or gasoline storage.
As Mark says… must be sealed combustion chamber, also known as FVIR to rest on the floor.
If that’s a screen in the base, it indicates that the water heater is Flamable Vapor Ignition Resistant (FVIR), which in some jurisdictions are allowed to be installed in a garage without the typically-required 18" height requirement.