ITE GFI breaker installed. Black wire shown, brown wire from the circuit. 2 white wires are about 6 inches long, tied back together with a wire nut inside the panel…
I’m wondering if someone tried to rig this so that it wouldn’t trip, or if it even powers anything. Or if it bypasses the "“breaker” function of the GFCI. With the homeowner’s OK, I pressed the TEST button, but the breaker didnt trip…Regardless, I called it out as needing replacement by a licensed electrician.
Nothing really wrong with the two neutrals being connected together, typically the striped neutral goes on the neutral bus and the white one is for the branch circuit neutral. I’m guessing that the wire nut is there to cover the bare ends on the conductors.
In this setup the GFCI will not provide any GFCI protection but will still function as a normal circuit breaker. Also the test button will not function. If this circuit does not require GFCI protection it can function as is.
Thank you Robert - I thought that may be the case - which explains that the test button did nothing. I guess it’s not “unsafe”, but is not installed correctly to provide GFCI protection. Thanks for the answer!
I don’t need to list them. I pointed them out. I could have said nothing and a new inspector might use this panel as an OK example. They need to think about this. I did half the work.
You however are not new and should know these simple material defects.