Would anyone recommend additional post/beam support?
That would be an improper post to beam attachment in my report. The beam isn’t bearing on anything
Very improper.
This picture is an improper way.
Chris,
Are those bolts just holding the beam together?
From the pics it looks like the beam is sitting on top of the 4X4’s and not bolted to the 4X4’s.
That connection is prohibited in the 2009 IRC deck code. And the posts should be 6x6’s.
Yes I agree! notched to hold the beam.
Beams bolted to post.
Also to other comments I’m well aware of the notched 6x6 requirement, unfortunately that’s not how this deck was built.
So Chris, out of curiosity, what did you put in your report?
Agreed, that beam to post connection is prohibited. Notching is allowed as Kevin Wood says, but notching is a pain. I prefer a Simpson “Strong Tie” Cap/Base (BCZ) to attach the post to the beam. Looks like the posts are buried in the ground. That’s not allowed in my jurisdiction. The posts have to be on 9" piers, 4 ft deep, and 6" above grade.
Recommend to strengthen support at post/beam at All post, including center post. Where two beams intersecting above one (center) post you may want to install a cleat down the side of the post. To install a cleat you will lay a short section of 2x4 flat against one side (inside) of the 4x4 support post flush with the top of the post and even with the bottom of the beam. Use a series of lag bolts to secure the cleat down the side of the post. This technique is used to expand the contact bearing of beams at the top of the post. Make sure the cleat is long enough and has enough bolts to pick up its share of the load, 3 feet is usually long enough. Note: Modern recognized building standards require All support post to be at minimum a 6" x 6" notched post; with beam resting on post.
Post are on concrete footing, attached with approved post base brackets.
Thanks for the info. Looked like the posts were just set in the ground.
I agree, surrounded by decorative rocks, post base was just a few inches under rocks. I moved some away and probed with screwdriver.
Hold the cleat with Lag bolts? Lag bolts? Didn’t you mean finish nails?
We have rule on the MB Chris provide a link!
http://www.strongtie.com/ftp/fliers/S-DECKCONTP12.pdf:mrgreen:
No. I don’t feel finish nails would provide proper strength.
Besides there were already enough nails holding this deck together; at post/beam and at ledger/band joist. ![]()
“If you need to expand the bearing for a beam, especially in situations where you have two or more beams intersecting above one post you may want to install a cleat down the side of the post. To install a cleat you will lay a short section of 2x6 flat against one side of the 6x6 support post flush with the top of the post and even with the bottom of the beam. Use a series of lag bolts to secure the cleat down the side of the post.”
[size=2][size=2]www.decks.com/deckbuilding/Post_Beam_Connections](http://www.decks.com/deckbuilding/Post_Beam_Connections)[/size]
[/size]
I’m on my iPhone. Not sure how to link stuff on it. Do you know how?
it may not be conventional but I think an engineer would say it satisfied shear strength requirements. just my opinion. I think it looks fine
I only find the 2009 just now:http://www.awc.org/Publications/DCA/DCA6/DCA6-09.pdf
Robert you are saying you wouldn’t write it up?