Originally Posted By: bbadger This post was automatically imported from our archived forum.
He is mistaken, note the last sentence of 110.14(A)
NEC
Quote:
110.14(A) Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors.
Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.
If the terminal is identified for two you may use two.
-- Bob Badger
Electrical Construction & Maintenance
Moderator at ECN