Inspected a 3 unit condo (new construction) and the service drop goes to the weatherhead at the same level as the 2nd floor (my client’s level) back porch deck.
I could easily reach out and tough the conductors without even touching the railing. Drip loop bottom was 4’11" above the porch deck floor level.
The back porch (structure) is steel and the decking is treated lumber.
Remember, this is in Chicago, where the porches themselves are dangerous :mrgreen:
One point is that the POCO hooked up to it. You would think that they would not have if it was bad. Probably like the idea of not haveing to use a ladder or basket. Just connect it from the back porch.
2003 IRC E3504.1 Clearance from building openings. Open conductors and multiconductor cables without an overall outer jacket shall have a clearance of not less than 3 feet (914mm) from the sides of doors, porches, decks, stairs, ladders, fire escapes and balconies, and from the sides and bottom of windows that open. See figure E3504.1
I can scan and post the figure if needed.
Maybe I misunderstand the photo. I was under the impression that this picture was taken while standing on a 2nd floor balcony. The cables would then be somewhere around 15’ off the ground below so the >10’ requirement above a walkway would be met it would seem. Now, I’m not sure what the technicality is regarding ‘sides of these areas’. It would sure seem to me that the cables don’t meet that requirement at all. They are “along side of those areas”, aren’t they? If this photo is taken from ground level then never mind, my assumption is wrong.
Stairway leads to access for a 2nd Floor apartment. Service cable is attached at the top of the Stairwell (Fire Escape) just above and to the left of the entry door.
This is After the Repair was Completed.
Work performed by a Licensed Electrician.
Permitted and Inspected by the Local Municipal Inspector.
Underwriter Seal from the Independent Electrical Inspector was affixed to the Main Panel confirming code compliance.
Some inspectors may not be aware of the code sitations that have been posted.
This is a very good question by the OP and as an inspector myself, I would not pass any of the 3 different situations presented by the different posts here on this thread.
Good catch by you guys!
That’s because in many areas the AHJ is only a general building inspector and may or may not be up to speed on all of the trades. Just this month I saw a county inspector pass a subpanel that had grounds and neutrals mixed, no panel bond, 3 neutrals crammed into each hole, and no ID on the neutral. They (HO) had ran a 4 wire feed but didn’t understand how to make it up at the sub. All he said was to clean out the drywall dust at the bottom of the can.
If we pull an electrical permit, we get an electrical inspector, who will know his stuff (and then some).
He will go strictly by the NEC.
But for a new house at final, we will get a general inspector who will go by the IRC.
Realize, when you cite “code” most people (especially the general public) asume you are talking about their own particular AHJ code.
In Illinois, any municipality over 10K population has the ability to set their own, local, code. I have seen villages, right next to each other, that have totally different ‘codes’ and some even contradict each other (like right across the street, fer gosh sakes!).
Chicago is the 900 lb gorrila, around here. To be a licensed electrician in Chicago and many of its surrounding suburbs, you HAVE to be union educated and a member of the union (IBEW) to even be considered to sit for the exam.
Thus, we have requirements like these:
All wiring (including low voltage, except 12V or less, DC, in EMT.
No “Mini-Breakers” (a device that fits in one panel lug, but has two seperate breakers).
AC whips of 3’ or less only.
No requirement for distribution panels (like in condos) to have a floated neutral. (as in bonding of ground and neutral only at the SE).
No requirement for bonding jumpers over water meters (most houses do not have water meters.
I have seen old 60 amp drops with 60 amp meter boxes (and SECS) with 200 amp panels. The codie says its OK.
My point is that the general public believes that “code” (i.e. local code) inspections are good enough. They don’t care about the NEC or changing safety standards, and neither do most sparkies around here.
BTW: In my example, the builder and his electrician and the local AHJ said this was OK. Why? Because they said that Commonwealth Edison hooked it up, so it must be “Code”.
How do I explain this to my client is someone gets zapped?
Hope my calling it out as wrong gets me off the hook with the jury.
For your purposes, If you can stand, stoop or lean over anywhere and touch a service conductor it is a hazard. Let the sparky who evaluates it figure out where the violations are.