Jacuzzi motor bonded or not?

No. Yes. Yes. No.

1 Like

Actually, your first No is incorrect.
“Pure” and “Distilled” waters Do Not conduct electricity (see my post again).
All other waters DO likely conduct electricity due to the mineral and impurity content. :wink:

Please help clarify…Have a Master bedroom located jetted tub with two pumps. One is inaccessible and unable to be seen the other has a bonding lug that is on the far side of the pump motor and this one has metal parts to the motor housing. The tub has all plastic piping around the tub. BUT when I went inside and voltage tested (one lead from the bathroom receptacle hot, and the other lead to the metal jetted tub spout, I was reading 101 volts. My question is: Do these motors need to be bonded at all? Visually, I can’t see any metal piping, but I can not see (don’t have access to) the stubs to the faucet handles. The original installer only put in a 12 x 12 access panel on the outside of the house.

Was it connect to a GFCI?

With all plastic piping there is no metal piping in contact with the circulating water so no need to bond.

1 Like

So the pump itself is plastic also?

The pump is connected to the EGC of the branch circuit. Equipotential bonding would be for other metal parts, if there are no other metal parts then there is nothing else to bond to the pump motor.

1 Like

So that ‘bonding stud’ that is visible on most every pump that I see is there for convenience as needed, not for necessity for the pump itself. Thanks for clearing up that ‘gray area’ that is oftentimes baffling.
On the surface, Jim’s comment seemed a bit simplistic for such a convoluted subject, thus my reply to him as being facetious.

That’s correct. The pump itself is bonded by the EGC. The lug on the motor is for equipotential bonding if required. I’ve seen guys run a #8 from the pump all the way back to the panel.

1 Like

Even if bonding is needed it does not need to go the the panel.

All electric home with PEX/plastic plumbing. What is the bonding point?

That’s correct and it is specifically mentioned in 680.74 that the connection to a remote panelboard or the service equipment is not required.

The way I am reading their replies, there is not a bonding point since bonding wouldn’t be needed in you scenario???
Would love for one of them to answer/ clarify you question for confirmation. This was a good thread!

1 Like

I may be a bit redundant, but I believe the bonding requirement would be determined by the AHJ. From Jacuzzi’s installation manual for walk-in tubs and whirlpool tubs:

“A pressure wire connector is provided on the exterior of the motor/pump and heater to permit connection of an No. 8 AWG solid copper bonding conductor between this unit and all other electric equipment and exposed metal in the vicinity, as needed to comply with local requirements.”

Frankly, I find more installation problems with the tub’s 15 amp protection requirements being connected to and protected by a 20 amp breaker or GFCI receptacle. And the lack of a separate circuit for the heater if installed.