Originally Posted By: rmoore This post was automatically imported from our archived forum.
Pretty colors!
Jay...when you post something like this could you give us a little info on what the panel is (service equipment, other, etc) and what type of home it's located in?
Anyway...
3 double tapped breakers.
Some of the wires look a little the worse for wear...I did notice the red from the tandem breaker appears damaged
Nasty little flammable "price tags".
If this is NOT the service equipment, and all the metallic conduit is "continuous" and used for grounding, I'm not sure what is else is wrong.
What am I missing?
-- Richard Moore
Rest Assured Inspection Services
Seattle, WA
www.rainspect.com
Originally Posted By: phinsperger This post was automatically imported from our archived forum.
Flamabale material
Double taps
Continous EMC?
If service panel then missing neutral/ground bonding
missing insulation from orange conductor
also;
6) I count 5 - 220V circuits. At least 1 is a 110/220
__I count 22 - 110V circuits.
__I count 16 - neturals
__So either there are some missing neutals or missing breaker ties for 3 more 220V circuits
Originally Posted By: bbadger This post was automatically imported from our archived forum.
I am not sure I see anything, other than the damaged wire.
This is not a service panel, there is no main breaker.
This is a Square D panel the breakers are listed for two wires.
EMT is an acceptable grounding conductor.
I have never been called for using the paper tags, most inspectors like having the labels.
I did not bother to count but if there is a 'shortage' of neutrals it is most likely because some of the circuits are sharing neutrals (Multiwire branch circuits) and handle ties are not required for that unless both circuits run to one 'yoke' or device.
Nothing wrong with the colors, kind of pretty.
If you look carefully at the bottom right hand corner you will see a bent piece of dirty copper, that would have been the bonding strap if it had been needed.
Can you tell us what you think is wrong?
-- Bob Badger
Electrical Construction & Maintenance
Moderator at ECN
We hope it's not the service panel! My guess would be a condo...but that's why I asked for more info.
Might be a Square-D panel but the breakers may not be(?). Don't most Square-D brand breakers have some visible labeling? These look suspiciously like off-brand breakers to me...which don't have the 2-wire capability. I'll remove my objection to the double-taps if they are the two-conductor rated breakers, but I can't see the terminals clearly enough in the photo.
-- Richard Moore
Seattle, WA
www.rainspect.com
Originally Posted By: Greg Fretwell This post was automatically imported from our archived forum.
QO breakers are certainly older than 1974 and I doubt there was anyone “knocking them off” in those days. I still have some mid 70 QOs left over from a big remodel I did in 75 (I bought several boxes). They don’t have any visible SqD logo when installed. It is on the side with the interupting rating. “SWD” (switching duty rated) is on the other side. The label indicating 1 or 2 conductors is in the wiring cavity in tiny font
BTW it says
1 or 2 AL/CU #8-14 if you left your microscope in your other suit. I do have a halfway decent picture of it.
Here’s an old 15-amp breaker I took out of my own Square-D panel a few years back (actual age unknown).
[ Image:http://www.nachi.org/bbsystem/usrimages/o/offbrand001.jpg ]
The only Square-D marking is a rather crude and "skinny" version of the Square-D logo. I don't know if this is an actual Square-D or a knock-off...but either way...
Originally Posted By: jschwartz1 This post was automatically imported from our archived forum.
Guys, it is a Square D Panel. The service drop to the mast is in deplorable condition. The insulation around those wires are cracked and wire is exposed. The service mast is only 8 feet above the ground.
Greg Fretwell wrote:
BTW I have never seen a 15 or 20a QO with the set screw terminal like the first one you showed. Is that a single pole 30?
Hi Greg,
No...it's a full size 15-amp, the only one I kept. I pulled a bunch of these (15 and 20s) out of an older Square-D QO panel when I replaced it about 4 years ago. I do not know the age of that original panel, but I would guess 20+ years (tossed now). All my new QO breakers (some from the old panel) have the indicator window, front labeling, and the 15 and 20 single poles now all have the 2-wire capability (unused  ).
I don't know if the one I pictured is a generic knock-off or just an old Square-D with a single-wire set screw. As I indicated earlier, I'm suspicious of the un-trademarked logo. Unfortunately, the paper label by the screw is totally illegible.
Anyway...from personal experience, I know that there are single-pole 15 and 20 amp breakers out there that look like Square-D, but are not designed for 2 wires. I don't see that many double-tapped breakers in Square-D panels but, when I do, I check the terminal type rather than just relying on the panel or breaker brand. The difference is very obvious from the right angle.
In Jay's photo, the double tap on the left does appear to be entering a central hole rather than either side of a grooved pressure plate...but who knows without actually seeing it from the side?
-- Richard Moore
Seattle, WA
www.rainspect.com