Light Switch Near Shower

The position of the switch and labeling has to do with it being WITHIN the shower itself and nothing to do with the original question or post. If shower is a manufactured shower kit and it has a built in switch and light, changes are they want it GFCI protected and the NEC clearly says if the switch is build into the shower as part of the kit…no problem as it would be designed to not create a hazard.

**404.4 Damp orWet Locations. **A surface-mounted switch
or circuit breaker in a damp or wet location shall be enclosed
in a weatherproof enclosure or cabinet that shall
comply with 312.2. A flush-mounted switch or circuit
breaker in a damp or wet location shall be equipped with a
weatherproof cover. Switches shall not be installed within
wet locations in tub or shower spaces unless installed as
part of a listed tub or shower assembly.

I understand Paul. My point is that we shouldn’t “make things up” when reporting or commenting on certain issues. I find it “interesting” that some inspectors feel it’s appropriate. . .

I gotcha Jeff…my post was not towards your post. It was towards the listing statement of showers with built in switches…nothing more fella…:wink:

Yes, please stop it will only confuse people. :sarcasm:

Paul,

When bathrooms get painted, the switch cover usually gets removed and the non-conductive coating on those metal screws holding the cover sometimes peel’s off exposing bare metal.

As for your comment about someone entering a shower to turn on the light …how about someone turning on the ceiling heat lamp while leaving the jacuzzi or adjusting the heater’s thermostat while in the tub…

In my opinion, the Canadian Electrical rule limiting the location of switch (s) in bathrooms is potentialy life saving.

Regards,

Yes,and i could win the lotto if i played, we could fall out of the sky in a plane and I still have a chance to be president. You have painted pictures of limited speculation. There is no data showing an increased risk of death from a light switch near a tub/shower space. If HI’s wish to call out probable cause the be ready to face the outcome is all i am saying. If the covers are off and someone takes a shower and touches a screw which should not have current on them anyway…then you cant fix stupid…As for the hot tub question, again insulated switch and screws are the majority…not the minority.

Please feel free to report as everyone deems fit…I am only answering questions as asked and I base mine responses on the minimum safety standards.

Please post the incidents where anyone was injured from having a switch within 3 ft of the shower or tub.

Boy, you’re tough Mike :wink:

Take a look at this reference :mrgreen:;

404.8 Accessibility and Grouping.
(A) Location.
(2) [OSHPD 1, 2 & 4] Switches shall not be installed within shower rooms or stalls or be accessible from within these areas. Switches shall not be installed within 5 feet (1.52 m) of the perimeter of bathtubs.

So you want to apply a requirement for hospitals to residential.;-):roll:

Just felt like adding to the confusion :smiley:

Trouble maker:mrgreen:

Maybe HIs should be recommending hospital grade receptacles too. :wink:

Don’t forget to mention the lack of a rubber mat in that same bathtub as well.

Guys, It just comes down to one thing, if you can reach the switch from the shower and there is a grounding problem you can die by electrocution. However, if the switch surface is plastic or non-conductive,which most are,and the box is grounded behind the cover, which most are, unless you have an uninformed (unqualified) electrician and a lousy electrical inspector or a very creative person, the chances are slim, very slim, that anything would happen to someone who reached the switch. What normally happens in these situations is that we would try to make the situation never happen,our code requires not being able to reach the switch from an area that is in contact with the water or shower area. As everyone knows,except insurance companies, there are people in the world who are not conventional and no matter what you do,seem to, unwittingly,do whatever is necessary to defeat any safety measures designed to protect them.

Absolutely!

**All personnel stationed on an aircraft carrier are given safety lectures and demonstrations. In 1990, a First Class Petty Officer assigned to the mess deck was briefing new junior personnel on electrical safety. He showed them how to fill out a warning tag on circuits undergoing maintenance, and informed them that they were forbidden to work on the circuit until a second person had double-checked the tag and circuit. In a prime demonstration of why the rules were in place, he proceeded to open and grab a circuit that he supposed was de-energized, killing himself in front of 20 thunderstruck students. **

http://www.darwinawards.com/

WHAT…Pope a trouble maker…say it is not so…say it just is not so…lol;-)

ok…this is just getting silly now. Lets not forget to report about squeeks on door hinges also while you are at it. Oh and that everytime you walk over to change the channel on your TV it could shock you…oh wait…can you even change a TV from the set itself anymore…all mine have remotes…lol

Lightning could strike me also as I walk down the street but I am not going to alter my life over it…it happens. Again we can’t fix stupid and if people do stupid things they are gonna get hurt…it is like weeding out the gene pool so to speak. A sad but true fact…

It seems that we are not the only ones discussing this issue!:stuck_out_tongue:
NOTE: The “Red Fonts” are mine!

http://www.inspectionnews.net/home_inspection/electrical-systems-home-inspection-commercial-inspection/6738-light-switch-proximity-bath-tub.html](http://www.inspectionnews.net/home_inspection/electrical-systems-home-inspection-commercial-inspection/6738-light-switch-proximity-bath-tub.html)

04-07-2008, 07:00 AM
Richard Franklin](http://www.inspectionnews.net/home_inspection/members/richard-franklin.html)
Member

Join Date: Mar 2007
Posts: 11
Re: Light switch proximity to bath tub
Attached is a drawing from Code Buddy. What is forgotten is the tub zone. The location of the switch or outlet within the tub zone has been an issue for many years. Mike Holt should be leading the charge to the NEC to change this situation. GFCI’s fail. People build up a false feeling of security. If a switch or outlet is not allowed within five feet of a pool or spa, how is it that it is allowed around a tub? Are you not just as dead?

If someone is not citing code issues,

isn’t this a cop out? It’s time that all HI’s studied the code and became experts. If you are not citing the code just what are you doing? Reporting the chipped paint? Broken window?

This is an issue that should be clearly addressed by the NEC. HI’s should be leading the charge. What we continue to have is a work force that is trained in a 3rd world country making life and death decisions. In the cases of new construction it would just as easy to move the outlets or switches.

04-07-2008, 07:04 PM

Jerry Peck](http://www.inspectionnews.net/home_inspection/members/jerry-peck.html)
Member

Join Date: Mar 2007
Location: Ormond Beach, Florida
Posts: 11,693
Re: Light switch proximity to bath tub
Quote:
Originally Posted by Richard Franklin
Attached is a drawing from Code Buddy. What is forgotten is the tub zone.
From the 2008 NEC.

  • 410.10 Luminaries in Specific Locations.
    • (D) Bathtub and Shower Areas. No parts of cord-connected luminaries, chain-, cable-, or cord-suspended luminaries, lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold. This zone is all encompassing and includes the space directly over the tub or shower stall.
      Luminaries located within the actual outside dimension of the bathtub or shower to a height of 2.5 m (8 ft) vertically from the top of the bathtub rim or shower threshold shall be marked for damp locations, or marked for wet locations where subject to shower spray.

You will notice that this section is under “Luminaries in Specific Locations”, not switches or receptacles.
Quote:
The location of the switch or outlet within the tub zone has been an issue for many years.

For receptacle outlets, the reference is: (underlining is mine)
From the 2008 NEC.

  • 406.8 Receptacles in Damp or Wet Locations.
    • © Bathtub and Shower Space. Receptacles shall not be installed within or directly over a bathtub or shower stall.

For switches, the reference isunderlining is mine)

  • 404.4 Damp or Wet Locations.
    • A surface-mounted switch or circuit breaker in a damp or wet location shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2. A flush-mounted switch or circuit breaker in a damp or wet location shall be equipped with a weatherproof cover. Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
      Quote:
      **If someone is not citing code issues, isn’t this a cop out? It’s time that all HI’s studied the code and became experts. **

Citing the correct reference is VERY IMPORTANT also.
Quote:
This is an issue that should be clearly addressed by the NEC. HI’s should be leading the charge.

I agree with that statement.


Jerry Peck, Construction / Litigation Consultant
Construction Litigation Consultants, LLC ( www.ConstructionLitigationConsultants.com](http://www.constructionlitigationconsultants.com/) )
www.AskCodeMan.com](http://www.askcodeman.com/)

04-08-2008, 01:10 PM

Jerry Peck](http://www.inspectionnews.net/home_inspection/members/jerry-peck.html)
Member

Join Date: Mar 2007
Location: Ormond Beach, Florida
Posts: 11,693
Re: Light switch proximity to bath tub
Quote:
Originally Posted by Aaron Miller
ECJ:

So, what are you saying then, that a “zone” is a “stall” and that these two words are synonymous?

What I was saying was simply that the code did not stated what Richard F. said, the “zone” only applied to light fixtures: “You will notice that this section is under “Luminaires in Specific Locations”, not switches or receptacles.”

And that switches and receptacle outlets were addressed separately (and differently).

I would like “the zone” to be applicable to all such installations (lights, switches, receptacle outlets) for ease of understanding what is allowed / not allowed where.

When I was working with Mike Holt on his 2005 Changes to the NEC video in late 2004 we discussed this, and the wording is very poor, it actually allows things which we would think were not intended to be allowed.
Quote:
And are you advocating, even given that a “zone” is not a “stall” per se, the any switches or receptacles located outside the stall yet in the zone be equipped with raintight corers?

What I was advocating was that if one is to quote the code, and was to chide other HIs for not quoting the code, that such person should actually be quoting the correct code themselves.

Here is an example of very poor code language:
From the 2008 NEC.

  • 406.8 Receptacles in Damp or Wet Locations.
    • © Bathtub and Shower Space. Receptacles shall not be installed within or directly over a bathtub or shower stall.

“shall not be installed within or directly over”

Come on now, “within”? Who is going to install a receptacle outlet “within” a tub? Crimney, it would be submerged whenever the tub was filled.

Or “or directly over”, as in “in the ceiling”, or as in "directly over in the walls? What if the walls are set back a few inches from the tub? Those receptacles are no longer “directly over” a bathtub.

A shower stall (or tub with a shower as the shower curtain/enclosure defines ‘the shower stall area’, that’s a lot easier to define and defend.

But at a tub with no shower, is that now even a “wet area”?

All I can do is raise questions on what it says. Mike was going to submit a code change for that, but I don’t know if he ever did, I was also going to submit a code change for that, but I never did - got busy with my business and forgot about it.


Jerry Peck, Construction / Litigation Consultant
Construction Litigation Consultants, LLC ( www.ConstructionLitigationConsultants.com](http://www.constructionlitigationconsultants.com/) )
www.AskCodeMan.com](http://www.askcodeman.com/)

Marcel,
The 8-foot high and 36-inch from the outside edge of the bathtub rule is just good old common sense! This DOES NOT show ANY switches within that zone!

It was put there for a reason!
http://www.nachi.org/forum/attachments/f19/29145d1244615162-light-switch-near-shower-bath-elect.jpg

Jeff,
WITH ALL DUE RESPECT… if you are going to quote code then… you should quote ALL of it!:wink:

FROM THE NATIONAL ELECTRICAL CODE.

2008 National Electrical Code
ARTICLE 404-SWITCHES
404.4 Damp or Wet Locations.
A surface mounted switch or circuit breaker in a damp or wet location shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2.
A flush mounted switchor circuit breaker in a *damp *or wet location shall be equipped with a weatherproof cover.
[FONT=Arial][size=3]Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly
[/size][/FONT]
{Below is all you posted …It seems that you left a lot of the code out of your quote!}:wink:
Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly

I hope that this information has been of some help!:stuck_out_tongue: