tcameron
(Thomas Cameron, South Carolina Home Inspector License 49149)
Hi All,
Found this panel this morning full of debris and rust/corrosion on wiring.
There isn’t a main disconnect breaker for the main service panel. Does the six disconnects rule apply here ?
The panel is a GE TL2020RH if that matters.
This panel feeds a sub panel inside the home.
Thanks
Tom
ccurrins
(Christopher Currins, CMI®)
4
What is the 100 amp breaker for?
tcameron
6
One is for the inside panel, the other for a shed…
kshepard
(Kenton Shepard, CMI)
7
That rule always applies but this panel is not in violation of that. Those two 30-amps are handle-tied so 6 hand movements would shut it all down.
jpope
(Jeffrey Pope, CMI, CHI, CPI, ICC)
9
Kenton is correct.
Let me rephrase this for you.
“There isn’t a service disconnect. Does the six-throw rule apply here?”
“Main” and “service” are synonymous, so calling something a main service is redundant.
The only clarification I would make to Kentons post is with the statement of “six hand movements.” It’s a common term, but can be misleading.
The rule is “six or less breakers/switches or sets of breakers/switches.” In theory, that could be one “hand movement.”