Hey Guys,
Should separate grounding wires be connected to each panel when there are 2 electric panel boxes with separate feeder cables from the meter?
Both panel boxes were 200a with a 200a main breaker with 3 conductor feeder cables from the meter.
I indicated in my report that each panel requires a grounding wire because only the panel on the right had a separate copper wiring grounding to a copper water pipe.
Best regards,
-- Mike Rose
Cornerstone Home Inspection Co. LLC
Lawrenceville, GA
Originally Posted By: jfarsetta This post was automatically imported from our archived forum.
Yes, two grounds are needed, with one to each panel. They can have a common source. Typically, a distribution trough may be found between the meter and panels. Here are some photos of a similar setup. 400 amps to 2 - 200A panels…
Originally Posted By: dvalley This post was automatically imported from our archived forum.
Joe,
What's up with the white wires being used as a hot and not taped up with black tape.
Sorry...I just had to bust _alls. ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif) ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif) ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif) ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)
Originally Posted By: mrose This post was automatically imported from our archived forum.
Joe,
Thanks for the consultation. Your pictures of the dual panel boxes are what I inspected. The only difference was the left sidi box did not have a grounding wire attached.
Best regards,
-- Mike Rose
Cornerstone Home Inspection Co. LLC
Lawrenceville, GA
Yes, folks, a real house. Realtor had to make the beds and pick food up off the floor before she dared show this dog to any prospective buyers. No, I didn't inspect the air handlers. I excluded them from the scope of the inspection.
Biggest problem in this house was the casement windows. When the genius who stucco'd the house put the drip guards above the windows, he never bothered to check clearances. ALL windows in the home only opened about 1-2 inches maximum. Ya think there was an emergency egress problem, boys and girls?!!! Oh well...