Hi guys,
I’m a ‘newbie’ here, just working through he Internachi courses. Just finished the basic Electrical, and inspected my own panel.
I was hoping someone could verify that what I’m seeing here is correct?
Would just give a bit of piece of mind that I’m evaluating correctly.
Thanks!
Here’s my notes:
Attached are photos from a residential service panel containing the main disconnect (main panel) that I inspected. Here is what I found:
- Missing screw from the dead front
- Missing labels
- The top portion of the panel was inaccessible due to the wood enclosure. I was unable to inspect; the service entry conductors, correct bonding of neutral bus to the enclosure, or the grounding electrode conductors.
- There appears to be several branch circuits not currently in use (taped off) that should be properly removed and cover plates installed.
- There are multiple double taps on the neutral bus
- The lower right hand portion of the panel contained a 30 AMP dual pole breaker that appears to have #14/2 wiring which is undersized. It also appears to be utilizing both the black and white conductors as ungrounded (hot) conductors which should be indicated. Also, because there is only 2 conductors this circuit would not have a neutral (grounded) conductor. This is a very hazardous condition due to the lack of a neutral wire and undersized conductors.
I would recommend a full evaluation of the panel by a Licensed Electrician.