Today’s inspection was a new build and it looked as though the deck was built first and then the patio was poured around the deck. Has anyone seen anything like this? It appears to be pressure treated lumber so I’m thinking I don’t need to be concerned about the wood being in the concrete, however, I’m not sure since I can’t see what’s going on below the concrete. Also, does the concrete at the bottom deck step present a trip hazard?
AAAAnd, while we’re talking about the concrete, does the grounding rod present a trip hazard? It’s located on the sidewalk right in front of the main panel. Any thoughts on this would be appreciated!
Does that location utilize a Bldg. Dept. & Permits and AHJ inspections?
If so… did the Final inspection actually take place?
Or… did the Homeowner have the concrete poured after the CO was obtained to save money?
FYI… Ground Rods are required to be ‘Below’ grade level, (safety issue)… and absolutely NOT along a walking path!
Hey Jeffrey, It’s rural Alabama. The county does utilize Bldg Dept & Permits. I can’t say when the concrete was poured. They just finished up work so the client asked me to do an inspection before close on Friday.
Thanks for the ground rod refresher. “below grade” duh.
The first riser of the steps was buried in the concrete, not the bottom step is about an inch tall, it makes a good trip hazard.
I’m guessing the buyer asked for the concrete after the deck was built.
Also it doesn’t matter if the wood it treated, no wood on a structural structure should touch the ground or concrete. Water will just deep into the crack and soak into the wood, eventually the posts will rot out.
I don’t think this will pass inspection, but it might have already had the final before the concrete was put in.
Bloody mess.
Did the concrete patio slope properly?
Poor Masonry Clearance.
Poor Wood Clearance.
If the wall/slab is exposed to precipitation, over time the moisture is absorbed by the concrete or masonry may cause the wood to rot – unless that 1/2 inch of space is maintained.
Just my 2 cents.
Even if it is pressure treated lumber, moisture will get trapped between the concrete and the wood surfaces resulting in wicking the moisture and can cause rot prematurely.
Yes.
Another thing to consider, did they block the weep holes when they poured the slab?
Yes, it was a long report. Longer than a new build should have been. Thanks for the insights on the wood. It made sense that wood rot would be an issue, however, I’ve never seen an situation like this.
Yes, the patio did slope properly. The slab is exposed to precipitation as it’s an uncovered deck.
Hey Kevin, it’s hard to see, but that last line of mortar is where the rope wicks were.
Thanks everyone for the insight and the confirmation. It’s why I love this forum!
Yes, besides a trip hazard it’s a few code violations.
A typical ground rod is 8’ long and must in contact with the earth for 8’ so that is one issue. The do make 10’ ground rods but it’s unlikely that it’s a 10’ rod.
The rod clamp that is subject to physical damage must be protected.
The GEC cannot be strapped to the slab because it is subject to physical damage and must be protected.
They should have pounded the rod down and poured the concrete over it. As it is now if it’s less than 36" from the front of the panel enclosure it is in the working space for the panel. A few applicable NEC code sections:
250.53(A)(4) Rod and Pipe Electrodes.
The electrode shall be installed such that at least 2.44 m (8 ft) of length is in contact with the soil. It shall be driven to a depth of not less than 2.44 m (8 ft) except that, where rock bottom is encountered, the electrode shall be driven at an oblique angle not to exceed 45 degrees from the vertical or, where rock bottom is encountered at an angle up to 45 degrees, the electrode shall be permitted to be buried in a trench that is at least 750 mm (30 in.) deep. The upper end of the electrode shall be flush with or below ground level unless the above ground end and the grounding electrode conductor attachment are protected against physical damage as specified in 250.10.
250.10 Protection of Ground Clamps and Fittings.
Ground clamps or other fittings exposed to physical damage shall be enclosed in metal, wood, or equivalent protective covering.
250.64(B)(2) Exposed to Physical Damage.
A 6 AWG or larger copper or aluminum grounding electrode conductor exposed to physical damage shall be protected in rigid metal conduit (RMC), intermediate metal conduit (IMC), Schedule 80 rigid polyvinyl chloride conduit (PVC), reinforced thermosetting resin conduit Type XW (RTRC-XW), electrical metallic tubing (EMT), or cable armor.
The top of the concrete patio should not be less than 4 inches below the top of the foundation wall, and weep holes should be fully exposed and unobstructed above the patio surface. Water will likely seep behind the brick wall and rot the sill plate and band joists. This is a major problem and I see no easy fix other than ripping out the concrete.