Greg Fretwell wrote:
Bob, 310.15(B)(2) doesn't say anything about exempting "... single conductors or multiconductor cables are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing and are not installed in raceways..." when it points you to table 310.15(B)(2)(a).


OK I see what your getting at. ![icon_cool.gif](upload://oPnLkqdJc33Dyf2uA3TQwRkfhwd.gif)

That aside how many home panels have the room for a 24" or longer bundle?

Greg Fretwell wrote:
You caught me on the 300.34. Teach me to use the CDROM search


No worries, it happens to all of us.

I picked up on it as I could not remember a 300.34 at all which made me go look at it.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



Well I’m fixin’ to put a QO130 (SqD type 9 can) in my house. That is 29" tall so it would be easy to bundle 24" of wire in there but I did say this is more likely in a commercial panel.


The 10, 11 and 12 cans have plenty of room.


I will have splices in there too ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)

That's why I went for the bigger enclosure. I hope I can make it pretty enough to post a picture here. Now if I can just find the time. I wonder if Santa will bring me some minutes.


Originally Posted By: pabernathy
This post was automatically imported from our archived forum.



lol



Paul W. Abernathy- NACHI Certified


Electrical Service Specialists


Licensed Master Electrician


Electrical Contractor


President of NACHI Central Virginia Chapter


NEC Instructor


Moderator @ Doityourself.com


Visit our website- www.electrical-ess.com

Originally Posted By: jonofrey
This post was automatically imported from our archived forum.



Electrical humor! Funny! icon_lol.gif


Originally Posted By: gporter
This post was automatically imported from our archived forum.



Can you make that pic bigger Greg.


Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



The picturt was just of the bonding jumper in the original picture. It really does not blow up that well.


Originally Posted By: dvalley
This post was automatically imported from our archived forum.



While we are on the subject of neat electrical panels…here’s one I had a few months ago.






David Valley


MAB Member


Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



That is a beautiful job. icon_cool.gif



Bob Badger


Electrical Construction & Maintenance


Moderator at ECN

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



I almost hate to do this but…


Unless the panel labeling indicates the neutrals can connect to the equipment ground bar we may be looking at a violation.

From what I can see that grounding bar on the left is screwed to the steel enclosure and has no bus bar or conductor connecting it to the neutral bar on the right.

If that is true the panels enclosure is being used as a neutral conductor which is a violation.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: dvalley
This post was automatically imported from our archived forum.



Bob,


This is LSE. The SE was outside at the end of the building. It doesn't need the bonding strap.

It was a huge townhouse I did on the Cape. Beautiful...huh?


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



dvalley wrote:
Bob,

This is LSE. The SE was outside at the end of the building. It doesn't need the bonding strap.



Dave I did not notice that this was a sub panel.

So why does it look like white wires are running to the grounding bar???

![](upload://27lS2vEGwEMXs26EuSn8EFPo6SA.jpeg)


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: dvalley
This post was automatically imported from our archived forum.



There are white neutrals tied into the grounding bar, but I’m simply showing you’ll a neat panel.


I pointed that out and my client had told me that he would have that taken care of in two minutes.


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Cool.


It's surprising that a person with such obvious pride in their work would not know that the neutrals on the grounding bar where a violation.

It is a beautiful looking job.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Here is a picture of an electric room in a large NJ home.


It should make the Chicago crowd lose sleep. ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)

![](upload://m2EsLesu9r8QM3sYBcIcpPt9EO4.jpeg)


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: dvalley
This post was automatically imported from our archived forum.



WOW icon_eek.gif


This is in a home?

What type of home?


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



I only posted these pictures at ECN for a NJ electrical inspector, I do not have the particulars.



For more photos and info it will be easer to just follow this link. ![icon_cool.gif](upload://oPnLkqdJc33Dyf2uA3TQwRkfhwd.gif)


http://electrical-contractor.net/ubb/Forum5/HTML/001099.html


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



I like to loop a 4ga solid (or whatever 250.66 calls for) through all ground busses before I start building a service panel. I know that screw is legal but I like wire.


Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Greg Fretwell wrote:
I know that screw is legal but I like wire.


Tough to have confidence in a low grade 10/32 machine screw.

I always use a jumper between terminal bars, for me that will usually mean between multiple grounding bars in one enclosure.


--
Bob Badger