I could not find in the IRC any requirement to install expansion space between the roof sheathing. This house had asphalt composition shingles. Do you know of a requirement? Is it generally recommended? I have seen metal spacers installed, but not on this new $500K house.
Joe, the best way to tell is to ready the APA stamping on the sheathing itself, H clips are required if the lable says “sized for spacing”
Regards
Gerry
There are no IRC requirements for spacing wood sheathing that I am aware of. However, it is considered good practice to leave a 1/8" gap between sheets, and that is also “recommended” by APA … but it is not required.
Actually panels marked “Sized for Spacing” simply mean that they are slightly smaller to allow for the recommended 1/8" gap (see attached APA TT #055). It doesn’t mean that panel edge clips (“H-Clips”) are required … although there are types of clips that will help with properly spacing the panels.
Panel edge clips (or some other type of edge suppoprt like blocking) are only required for structural ratings with thinner panels and larger support spacing … like 3/8" sheathing on roof trusses 24" o.c. would require panel edge clips for support (See Item #7 under “Fastening Hints” on Pg-2 of the attached APA Guide #N335, and Footnote-d of IRC-Table R503.2.1.1-1 on allowable panel spans).
Hope that helps …
P.S. For those that dont have the IRC, see attached IRC Table R503.2.1.1(1) from one of the free online codes at www.iccsafe.org
Thanks so much Robert.