Does anyone see anything wrong with this aka sub-panel ? Neutrals and grounds on the same bus bar ? Bonded to enclosure ?



Does anyone see anything wrong with this aka sub-panel ? Neutrals and grounds on the same bus bar ? Bonded to enclosure ?



Yeap
I don’t see a panel bond, but the grounds are on the wrong bar.
The top left breaker looks loose or maybe wrong brand.
Bus bar is bonded to enclosure (see in last picture) I always get confused with this stuff sometimes
There’s a green screw and bonding strap. It took me a while to find it.
That screw should be removed ?
The strap need to be removed and a ground bar added. The grounds then move to the new bar.
Non compliant breaker in the box
I guess so.
Ummm…anyone notice the ground is not using all the strands in that Compact conductor…effectively not using the full conductor correctly.
Edit: My Bad…Old Age and Roberts Keen Eye…lol
That’s actually the EGC. ![]()
True Dat…Thanks for keeping me honest Robert…lol
BUT…the way this panel is installed as it sits…I AM technically also right if we call it a “Grounded” conductor…no separation…