Sometimes in a new service upgrade which would not comply with todays requirements…you have no choice but to relocate the service panel. Wel as noted the feeds to the old panel are still their…but you remove the guts, blank the door and label and rewire from the old panel to the new panel.
This is about all that can be done in some older installations…
Sorry to bring a dead thread back to life but I think my question fits. The panel in question is still being used as a panel but has a couple of junctioned wires in it. Would you write this up?
It is a sloppy mess for sure. Regarding splices - I know splices are permitted (extending a wire to reach a breaker as an example) but my understanding is that wires entering a panel, splicing to a wire, and exiting the panel (panel used as a junction box) are not. Can you confirm?
Panel enclosures can be used for pass though conductors or splices even when the conductors do not terminate to the panelboard within the enclosure. The 2011 NEC has added a new wrinkle where it requires labeling when used for pass though or splicing.
Well…I believe you have other issues in that Panelboard enclosure to write up. The NM Cable without being secured to the enclosure, the white conductor terminated onto a ir out breaker without RE-identification among other things.
Also we can assume you verified the bar between the EGC and Grounded Conductors is not connected together as well…can’t verify from photos.