Student Discussion: The 2021 International Residential Code® (IRC®) Exam Study Course
Thank you Tonja. I’m just finishing up an inspection this afternoon and will go in and upload my last assignment. I appreciate you hanging in there for me
Writing assignment # 18 * In what locations are arc-fault circuit interrupter protection mandated? E3902.21 Arc-fault circuit interrupter protection says Branch circuits that supply 120-volt, single-phase, 10-, 15- and 20- ampere outlets installed in kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreations rooms, closets, hallways, laundry areas and similar rooms or areas shall be protected
Water heaters located in a garage must be elevated a minimum of 18 inches above the garage floor. The exception to this would be the FVIR units first required on 30,40, and 50-gallon heaters in July of 2003. As always, HIs must be careful because the existing stock was allowed to be sold and may show up two or more years after the change was required
The maximum length of a clothes dryer vent hose after the unit connection is 35 feet. Each 45-degree elbow reduces this by 2 1/2 feet and each 90-degree elbow by 5 feet. The vent must exit to the exterior of the building, not in garages and crawl spaces, as we often find them.
Writing assignment #5 - * Under what conditions is an unvented crawl space permitted?
R408.1 Moisture control. The under-floor space between
the bottom of the floor joists and the earth under any building
(except space occupied by a basement) shall comply with
Section R408.2 or R408.3.
Hello,
Thank you to all of the NACHI staff who created my training. I am grateful for the amount of work that has gone into the CPI courses. I put a lot of effort into study and in my opinion, the NHIE is difficult. The information I am offering is for other students who are studying for NHIE
You can copy this study set and edit the flashcards or create and add to customize.
Benson created exam prep
I am not affiliated with Quizlet, but I enjoyed using it after mastering the Nachi practice tests and exams.
If the link doesn’t work, you can search
“Home inspector exam Benson”
If appropriate, it would be nice to start a post where recent test takers who are willing to share one question or two from the exam could relay that information to add to this study guide.
How do pinless moisture meters detect moisture?
Radio waves *
The purpose of the IRC (International Residential Code) and scope is to provide the minimum requirements for building 1 and 2 family dwellings not exceeding 3 floors. The minimum requirement’s must provide adequate information highlighting variables like structural, electrical, mechanical, plumbing and safety. One important things the scope covers, is who the building official is and what their responsibilities and liabilities are.
In reference to the question: When there is a conflict between a general requirement and a specific requirement, which provision shall be applicable?
The specific requirement trumps the general requirement. The code is designed to be a blanket that covers all of construction; However, certain requirements such as those listed under UL have specific design specifications that supersede the requirements as listed in the IRC.
  • What is the purpose and scope of the International Residential Code? The purpose of the IRC is to ensure codes are met with one to two family dwellings and no more than 3 stories above grade plane in height. Also to ensure structural safety, protection from the hazards of a fire, and life safety.
  • What is a dead load? A live load? Dead load refers to floors, roofs ceilings, stairways, finishes and so on. Live loads simply mean wind, snow and people living in the structure.
  • What is the minimum ceiling height permitted for a living room or bedroom? A hallway? Bathroom? Basement? Where can a reduction in such heights be acceptable? The minimum ceiling height for a basement, bathrooms, toilet rooms and laundry rooms, should be 6 feet and 8 inches. On the other hand for habitable rooms, hallways and portions of basement should be 7 feet.
A natural gas flue must terminate at least 5 feet above the last appliance connected to the flue. The overall height of the flue must be a minimum of twelve feet above the base of the losest appliance.
Gas shut off valves must be located in the same room as the appliance. The valve must be upstream from the union or flexible connector and it must be accessible.
Lavatory sinks require a 1-1/4-inch drain and trap, while kitchen sinks and garbage disposals require 1-1/2-inch drains and traps. floor drains must have a minimum of a 2" drain and must have a removable strainer.
Writing Assignment #6 - What are the limitations for notches in floor joists? Bored holes?
  1. Notching. A stud in an exterior wall or bearing partition
    shall not be cut or notched to a depth exceeding
    25 percent of its depth. Studs in nonbearing partitions
    shall not be notched to a depth exceeding 40 percent
    of a single stud depth.
  2. Boring. The diameter of bored holes in studs shall
    not exceed 60 percent of the stud depth, the edge of
    the hole shall not be less than 5/8 inch (16 mm) from
    the edge of the stud, and the hole shall not be located
    in the same section as a cut or notch. Where the
    diameter of a bored hole in a stud located in exteriorwalls or bearing partitions is over 40 percent, such
    stud shall be doubled and not more than two successive
    doubled studs shall be so bored. See Figures
    R602.6(1) and R602.6(2).
    Exception: Where approved, stud shoes are
    installed in accordance with the manufacturer’s
    instructions.
Writing assignment #7 - * Where must a bored hole in a stud be located? What is the maximum permitted size of a bored hole located in a bearing wall? In a nonbearing wall?
    instructions.
Writing assignment #8 - * How must roof drainage water be discharged? - R801.3 Roof drainage. In areas where expansive soils or
collapsible soils are known to exist, all dwellings shall have
a controlled method of water disposal from roofs that will
collect and discharge roof drainage to the ground surface not
less than 5 feet (1524 mm) from foundation walls or to an
approved drainage system.
In reference to writing assignment #3 * Where must illumination be located in relationship to interior stairways? Exterior stairways?
Interior stairways shall be provided with an artificial light source to illuminate the land- ings and treads. There shall be a wall switch at each floor level to control the lighting out- let where the stairway has six or more risers.
On the other hand, exterior stairways shall be provided with an artificial light source located at the top landing of the stairway.
M. Theresa Craig
TREC 20588
ICC exam 1
• What types of inspections are specifically required by the code? When are
inspections required?
• In new home construction, the inspections are performed in phases. Each phase shall be
inspected before completing the phase or before cover-up. The foundation shall be inspected
before placing the concrete and may also be called a rebar inspection or form board
inspection. Below grade plumbing and electrical are also installed at this stage. Phase 2 or
pre-drywall inspection is performed before installing the interior wall sheathing (drywall). This
inspection verifies construction according to the design, wall bracing and load transfer system.
It is also called rough-in or drywall inspection. Also included are inspections of approved
materials, installations of those materials which meet the requirements for fire prevention, and
their restricting flame spread properties, emergency escape, and systems rough-in. The final
phase inspection relies heavily on the thoroughly performed phase 1 and phase 2 inspections.
The final phase includes systems testing (HVAC, Plumbing, Electrical, Gas, etc.) and a blower
door test that checks for air infiltration. In some instances, construction in flood zones or
floodways require specific construction methods that require inspections.
Exam Question 1
  • How many egress doors from a dwelling are required? Under what conditions is an additional egress door required? What is the minimum required size of an egress door? The minimum should be one door, access to a public way or to a yard. When more ocupants are in the dwelling with 2 or more doors. The minimum height is 78 inches and measured opened at 90 degrees, from the face of the door to the stop is 32 inches minimum.