Originally Posted By: jpope This post was automatically imported from our archived forum.
I don’t believe that access to a panel in a crawl space could be considered “readily accessible.” Nor could the proper working space clearance requirements be maintained. I vote NO.
Originally Posted By: gbeaumont This post was automatically imported from our archived forum.
Yeah Jae,
reminds me of the time Dave Bush called to ask me some advise about an 8 ft high crawl space with concrete carpeted floor, wall panneling and a dropped ceiling 
Full basements are pretty rare in his part of the world, that was too funny  
Originally Posted By: jmyers This post was automatically imported from our archived forum.
Ok, here it is…
Article 110.26(E) States the 6 and 1/2 feet requirement that Jeff P. speaks of....
I agree with that....don't think you could argue that at all.
Under that however, there is an exception which Jeff P. did not mention.
It states:
Exception: In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6 and 1/2 feet)
I personally believe the intent of that exception would allow panels to be installed in basements which don't meet the 6 and 1/2 feet rule. However, whether inadvertant or not, it would allow the sub panel to be installed in the crawl space assuming the remainder of the code was followed.
Originally Posted By: dandersen This post was automatically imported from our archived forum.
Sounds like they are allowing sub-sub-panels, as I call them here.
Under 200 amps is a sub,sub-panel. They put them in attics as well.
I can see a panel (disconnect) in the space to handle equipment there.
I would call the code man on any "main" put there for access issues (as JPOPE indicated).
Originally Posted By: jmyers This post was automatically imported from our archived forum.
Gerry,
Don't you just hate it when they call you up with questions about those finished crawl spaces! 
Originally Posted By: jpope This post was automatically imported from our archived forum.
Quote:
2002 NEC, Article 100(I)
Accessible, Readily (Readily Accessible). Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to climb over or remove obstacles or to resort to portable ladders, and so forth.
Capable of being reached quickly for operation
I don't think a belly crawl through a hatch qualifies for this. . .