Originally Posted By: Thomas Ogryski This post was automatically imported from our archived forum.
Unless someone could produce the manufacturers documentation showing that this method is one of the allowable installation methods for this fan, I’d say that this is at least a listing violation (110.3(B) in the 2005 NEC) Manufacturers instructions are to be followed when installing equipment.
Another violation, IMO, is " 400.8 Uses Not Permitted... (1) As a substitute for the fixed wiring of a structure."
Originally Posted By: Greg Fretwell This post was automatically imported from our archived forum.
The most important issues would be how it is attached to the cord, to the ceiling and that the swag kit was the kind using a ground wire.
I don’t like swag kits but once you get out beyond the plug things really become a little fuzzier from an NEC standpoint. This is not part of the building wiring so the new owner can simply take it down if they think it is a hazard.