Originally Posted By: jonofrey
http://www.nachi.org/bbsystem/usrimages/D/DSC08163.JPG ]
system
(system)
2
Are those SE cables or a feeder on the load side of the disconnect?
It is wrong no matter what but if these are actually service conductors you ratchet the danger up a few notches.
This needs further evaluation, no matter what.
system
(system)
3
Well the line fuse finally burnt through so I was out of power for awhile. Not long, good response time.
Greg, that is a feeder on the load side of the disco. Thanks for your reply.
system
(system)
4
John, those look like THHN and do require a raceway system, along with a box for the tap. If they are USE they don’t belong in the house at all.
system
(system)
5
Originally Posted By: bkelly1
Why can’t the USE be in a house? My mind must fail me
I know it is not ideal, but what dangers exist?
system
(system)
6
system
(system)
7
Originally Posted By: Thomas Ogryski
USE conductors are not required to have flame retardent insulation.