The amperage rating of the sub-panel disconnect


The amperage rating of the sub-panel disconnect (30 amp)exceeded the amperage rating of
the feeder conductors (20 & 15 amp). is this correct or is it 30amp on each leg?

Where’s the pic of the innerds??

A 30 amp rated disconnect is rated to be supplied with up to 30 amps. The rating is the maximum it can be supplied with.

1 Like

Looks like the feeder is 30 amps and there are two branch circuits, 1-15 amp and 1-20 amp.

1 Like