Originally Posted By: egriffin This post was automatically imported from our archived forum.
A friend of mine is selling his house. Recently, he replaced his hot water heater and did not properly align the TPR with the copper pipe, so he joined them with a piece of radiator hose which clamp to the pipe. Is that okay or not?
system
(system)
June 30, 2004, 12:00am
2
Originally Posted By: dbush This post was automatically imported from our archived forum.
Ed, not it is not okay. Should be unobstructed 3/4" piping, preferrably PVC piping.
– Dave Bush
MAB Member
"LIFE'S TOUGH, WEAR A HELMET"
system
(system)
June 30, 2004, 12:00am
3
Originally Posted By: Blaine Wiley This post was automatically imported from our archived forum.
Quote:
preferrably PVC piping.
copper?
system
(system)
June 30, 2004, 12:00am
4
Originally Posted By: kmcmahon This post was automatically imported from our archived forum.
I didn’t understand the PVC thing either. Not sure I got the whole picture here.
–Wisconsin Home Inspection, ABC Home Inspection LLC
Search the directory for a Wisconsin Home Inspector
system
(system)
June 30, 2004, 12:00am
5
Originally Posted By: Guest This post was automatically imported from our archived forum.
I think he meant “preferrably NOT pvc”
system
(system)
June 30, 2004, 12:00am
6
Originally Posted By: ekartal This post was automatically imported from our archived forum.
Would CPVC be allowed?
Erol
system
(system)
June 30, 2004, 12:00am
7
Originally Posted By: dbush This post was automatically imported from our archived forum.
Thanks Chad.
– Dave Bush
MAB Member
"LIFE'S TOUGH, WEAR A HELMET"