system
(system)
October 9, 2005, 12:00am
Originally Posted By: cbuell This post was automatically imported from our archived forum.
Does anyone have a quick opinion as to whether non-underground romex is allowed in conduit that is underground? Doesn’t seem right to me.
system
(system)
2
Originally Posted By: bbadger This post was automatically imported from our archived forum.
No you can not use NM underground even in conduit it must be a wet location cable or conductor.
300.5(D)(5) Cables and insulated conductors installed in enclosures or raceways in underground installations shall be listed for use in wet locations.
-- Bob Badger
Electrical Construction & Maintenance
Moderator at ECN
system
(system)
3
Originally Posted By: joetedesco This post was automatically imported from our archived forum.
… and a Wet Location includes installations underground too as per the definition.
– Joe Tedesco, Massachusetts
Home Inspector Provider
www.joetedesco.org
necmeister@gmail.com
www.nachi.org/tedesco.htm
www.nachi.org/tedesco2.htm
www.nachi.org/illinoislicense.htm
www.nachi.org/jtarticles.htm
system
(system)
4
that is what I thought, thanks!
system
(system)
5
Just for the record, if the cable was Type UF “Underground Branch Circut and Feeder” type, it would be designed for use in a wet location, buried, and including within a properly sized conduit of metal or nonmetallic materials.
Sometimes when in a basement you will find a box used where the inside wiring is run to that box to feed the Type UF or underground conductors to the outside.
Take a look a Table 310.13 if you have a copy of the NEC. If not search for it on the net.
-- Joe Tedesco, Massachusetts
www.joetedesco.org
system
(system)
6
Joe,
Thanks for the info. The lack of change to UF was my first clue that they just kept running the same wire. Simple enough fix though.