Ignore the brick chimney on the right. It’s already a reported defect with an oil fired forced air furnace sharing the same flue as a supplemental wood fired forced air furnace. Creosote is type of liner, right?
I’m concerned at what height is a sectional chimney needs support? Guy wires or otherwise. This one measured from the high side is at 93". It’s a DLR (doesn’t look right) to me. Any suggestions? Thanks!
Below is what I say in my report along with the attached pic.
· **Repair:**The metal chimney should be braced in order to ensure it remains stable in high winds. Lack of bracing for taller chimneys can lead to collapse causing property damage and personal injury. Metal chimneys that extend five-feet or more above the roofline usually require bracing. A chimney specialist should be consulted to further evaluate this condition and provide repair/improvement recommendations.
Correct on both statements and part of the schooling for WETT Site Basic in Canada.
Even if they are both done right there must be at least 18" clearance between the two chimneys according to Canada CSA standard.
Greg,
I forget at the moment, as I don’t see it very often, but isn’t there something about two chimneys being at the same height when they are within a certain distance of each other? Aren’t they supposed to be offset?