Well one of the first things that needs to be replaced aside from fixing the junction box behind the oven is the Federal Pacific Electric panel, those red tip handles actually means red for fire danger… literally. 10 years ago a buddy of mine suffered a serious pole-barn fire that also involved paint and paint thinner, kerosene and gasoline cans, a riding lawnmower and similar equipment, well as the oxygen/propane cutting torch. There was an FPE panel I thought nothing of, and as I was unplugging the arc welder from a 50A surface mount receptacle with metal conduit to the panel, the receptacle had chipped away and the lugs came loose and touched each other and the metal box, both the 50 amp & the main breaker failed to trip, I fell with my T shirt on fire and crawled low to smother it out for about 30 feet or so to get out and call 911, during which molten metal was flying everywhere and eventually blew the primary fuse on the pole, the barn began to collapse before the fire department could arrive and I spent almost a week in the hospital with 1st and some 2nd degree burns on my chest, arms and stomach, I have permanent scarring as a result. I wouldn’t wish this on my worst enemy and hopefully my experience with FPE equipment with the scars to prove it should be more than enough to convince anyone with this panel currently in use to get it replaced ASAP without delay.

1 Like

Thank you, Bryce.
Very informative.

FPE (Federal Pacific Electric) panel defects primarily involve the Stabloc, which are known to fail to trip during overcurrents and short circuits, leading to a significant fire and electrocution hazard. Other issues include loose connections due to metal expansion differences between copper breakers and aluminum panels, undersized bus bars, and internal mechanisms that can remain “on” even when the switch is in the “off” position.

1 Like

Thanks for posting.
Could use some editing or a “cold open”, a bit long for an intro.

1 Like

This is why we DON"T turn the power ON when a home has been powered down. Personal injury (in the case of the sparky who didn’t explain WHY he was disconnecting the welder) or property damage can end your Home Inspection career or your life!

8 Likes

We should already know the explosive power of electricity. They teach this in Electrical 101, Chapter 1, page 1.

The moral should have been, “Why inspectors should not operate breakers”. Shame on this inspector. The arc flash could have easily been in the panel and in his face.

5 Likes

That breaker (s) should not have been turned ON. We don’t know why it was OFF.

7 Likes

I can say with a high degree of certainty that a box behind a stove did NOT cause the arcing at the service mast. This is yet another example of how little people understand about electrical systems and electrical troubleshooting. A little logic is needed. This is a classic example of the cum hoc ergo proper hoc fallacy in electrical troubleshooting.

First, the breaker that was turned on is midstream. Downstream of it is at least one other breaker. I said at least one because there would be a branch circuit breaker. Even when the outdoor breaker is the service breaker, the odds are that the interior panel also has a main breaker (though not needed). In that case there would be three breakers between the junction box and the service connection.

The service drop connection is upstream of the breaker that was turned on. There may have been a problem in the junction box behind the stove, but the probability of it being the cause of the arcing is virtually zero. The two or three breakers between the junction box behind the stove and the service point of connection are all rated for 10,000AIC (minimum). Transformers used for residential service are limited to 10,000A AFC. Thee breakers would trip in a direct fault almost instantly. If they didn’t, it would have been because the problem in the junction box would have had a high enough resistance that it would have taken a few seconds for the breakers to trip, but one of them would have tripped.

In either situation, or anything in between those extremes such as a higher resistance load that would not cause the breaker to trip at all or take several minutes to trip could not, there’s still the integrity of the conductors and connection further upstream.

Logic dictates that that the cause could not have been in the junction box behind the stove. In order for a problem at the junction box to cause arcing at the service drop, both, or all, upstream breakers would have had to have failed and a problem with the wiring integrity would have already existed. That’s three major problems that would all have to have existed in addition to the problem in the junction box behind the stove.

If there hadn’t been a problem already at the location where the arcing occurred, nothing downstream could have caused the arcing.

I’d like to know who said that the cause was at the junction box. If it was an electrician, that only reinforces what I have been trying to get home inspectors to understand for years. That is, that electricians are not trained to troubleshoot electrical systems and very little knowledge of electrical systems is required to be an electrician.

4 Likes

There was definitely more going on than just a loose connection in the outlet box. There was arcing in the meter box as well. Maybe @mmorgan31 would like to join the conversation and give us some insight.

1 Like

I just sent in a picture on my writing assignment of old wiring that is frayed and naked wire exposed, bird nests over the old insulators and thought of what could happen if not corrected. This video was very good to illustrate it. Thanks

1 Like