Originally Posted By: psisler This post was automatically imported from our archived forum.
I agree with Jerry. The, as I see it should be placed in an area that is free and clear to be able to access it in an emergency etc… Like an adjoining wall.
Originally Posted By: jtedesco This post was automatically imported from our archived forum.
Mike Parks wrote:
It is not allowed to be on the AC.
Mike P.
The disconnecting means is permitted to be installed on or within the air-conditioning or refrigerating equipment.
Also, make sure that the disconnecting means is not located on panels that are designed to allow access to the air-conditioning or refrigeration equipment.
Originally Posted By: jpeck This post was automatically imported from our archived forum.
Joe,
Assuming the a/c condenser unit is on the ground (not up in a tree or up on a deck) and then adding in the required working space already referred to (if that were done), then, yes it would be readily accessible.
However, because it does not have the required working space (which would make it readily accessible) so it is not readily accessible as it now is.
Correcting the main problem, the lack of required working space, would make this readily accessible, so that is a secondary issue, which is corrected by correcting the primary issue (working space).
Now, as to the disconnect on the unit, I was going to address than second, becuase it is (I feel) not the "first and foremost" thing wrong.
It is, as you stated allowed on or within the a/c unit, however, it is not allowed on access panels. The following is directly from the 2002 NEC Analysis of Changes CD (it's also in the book of the same).
I was going to add the graphics in line, but because it is a little large, I added it as a link for dial up users.
Originally Posted By: jpeck This post was automatically imported from our archived forum.
Mike Parks wrote:
The correct answer is B.
A supplemental ground rod is never required.
Mike P.
C. Sometimes
With a qualification.
It is the word "never" which makes the difference. Never is all inclusive, and your specific reference to asking about a "ground rod" is why you choose B, however, Supplemental Electrodes are required in some cases, and ground rods are one of the options to use for that REQUIRED supplemental electrode. Thus, there are times when the only available option may be the driven ground rod, and, being required (if it is within that requirement) that makes a supplemental ground rod "required" in that specific case. Maybe one shot in a million, but there is the possibility that all conditions could lead to that end.
Originally Posted By: jpeck This post was automatically imported from our archived forum.
Ryan Jackson wrote:
Mike: 440.14 says that you can put the disco on the unit.
Ryan,
Yes and no (as shown in my previous post above).
440.14 Location.
Disconnecting means shall be located within sight from and readily accessible from the air-conditioning or refrigerating equipment. The disconnecting means shall be permitted to be installed on or within the air-conditioning or refrigerating equipment.
The disconnecting means shall not be located on panels that are designed to allow access to the air-conditioning or refrigeration equipment
That last statement pretty much limits *where* on the equipment it can be mounted to those areas which are non-removable or are removable but does not provide access to the equipment (which is going to be hard to do - have a removable panel which does not provide access to the equipment, that's why it is removable, it's designed to provide access to that part of the equipment).