Why are these circuit breakers zip tied onto the panel?

Never seen this before. The first course of breakers are zip tied onto the main service panel. The 30 amp double pole is labelled “generator” and is part of a generator transfer switch set up. I am thinking this is a way to have the disconnect breaker attached to the panel? Any thoughts? I am having the clients get in touch with a generator install company/ electrician as the generator set up is very handy man style.

The generator breaker is back fed when on generator power and requires a clip, screw, or some other means to hold it in place beyond being snapped onto the bus stabs. Did the cover have the required interlock kit?

1 Like

The cover did, is this zip tie setup allowed? Usually see a screw or clip, never a zip tie. Thanks

IMO that is not a proper method but you would need to check with the panel manufacturer to see what they recommend. It looks like it’s meeting the intention of keeping the back fed CB in place so it’s a toss up as to whether or not it will be an issue. For older panels there might not be a commercially available product designed for that specific panel.

1 Like

I have seen one that came with a zip tie to hold the the breaker as required.