4 Point Inspection Questions
I asked this over on the emergency forum but to spread a wider net, had a question about some things I ran into on a 4 Point inspection.
The home is a 1973 build. During the electrical inspection, I located a couple of electrical outlets giving an open ground fault. Additionally, I found double and even triple taps of neutrals and grounds in the electrical panel. Also, I found evidence of aluminum branch wiring.
I checked the box for improper grounding, double taps (the neutrals and grounds…no double tapped breakers observed), and marked that I saw the presence of aluminum wiring. My client had an electrician come by to check on things, and he stated everything looked fine to him and that there is no problem with a 1973 house having double and triple tapped neutrals and grounds.
My three questions:
  1. Is the presence of double or triple taps of neutrals and grounds in the subpanel a hazard that is supposed to be indicated on the 4 Point inspection form? Or is this solely for finding double tapped breakers?
  2. Is the “improper grounding” hazard a box that should be checked if there are outlets I found that show “open grounds?” Are open grounds even within the scope of the 4 point inspection form, or is the improper grounding hazard box only for overall system grounding (no grounding rod, etc)
  3. All other potential issues aside, if you observed aluminum single strand branch wiring in the subpanel, is this enough to mark the electrical section as “unsatisfactory”?
I spoke with the person from my clients insurance who is reviewing the forms and she didn’t know the answer to these questions. Just trying to get a feel for how other inspectors in florida who complete 4 points are answering these questions.
Thanks
These are all really good questions. Ever find an answer?
  1. Yes. Double taps on breakers are largely inconsequential. They don’t start fires. Double tapped neutrals are much more hazardous. They start fires.
  2. Yes. Any improper grounding that you are able to identify is reason to check the box. A GFCI with an open ground is not a hazard, but it or any other receptacle outlets that are protected upstream should be labeled as being GFCI protected. The lack of a label, however, does not make it a hazard. FYI, you should avoid the use of the word “Fault” when describing an open ground. Fault has a very specific meaning in the electrical world.
  3. Yes, unless you can determine that the associated problems have been properly remedied. That would be outside your scope, but you could suggest to your customers that they provide evidence of the remedial work to their insurance company.